How do I model natural ventilation for LEED in EnergyPlus?

I have come across a couple projects located in South America where they are looking to model natural ventilation as the only HVAC system for LEED. This is addressed in Appendix D of the Advanced Energy Modeling for LEED v2.1 document for those who have purchased it but I want to double check my interpretation and see if anyone has used this method.

My understanding in this situation is that the Proposed HVAC system should be the same as the Baseline HVAC system with the airflows and capacities being identical to account for when the natural ventilation system can't meet setpoint, whether the building is designed for this not. Since the natural ventilation is bringing in the required outside air, there is no reason for the Proposed HVAC system to be running if there is no heating/cooling demand during occupied hours. So in this case, can you change the fan schedule to have the system only run when heating/cooling is required, not continuously during occupied hours as long as your natural ventilation is available? I'm assuming you can also set your Proposed HVAC outdoor air minimum to 0 since your are bringing in the outside air via natural ventilation, making it a return air only unit essentially.

Making this more complicated, if you're natural ventilation system has a min or max outside air when it becomes unavailable, your HVAC system needs to become available with your minimum outdoor airflow to meet setpoint. It seems that this could possibly be done through the EMS or be done post process.

Does anyone have experience with this process or be able to provide any insight on my understanding of it?

How do I model natural ventilation for LEED in EnergyPlus?

I have come across a couple projects located in South America where they are looking to model natural ventilation as the only HVAC system for LEED. This is addressed in Appendix D of the Advanced Energy Modeling for LEED v2.1 document for those who have purchased it but I want to double check my interpretation and see if anyone has used this method.

My understanding in this situation is that the Proposed HVAC system should be the same as the Baseline HVAC system with the airflows and capacities being identical to account for when the natural ventilation system can't meet setpoint, whether the building is designed for this not. Since the natural ventilation is bringing in the required outside air, there is no reason for the Proposed HVAC system to be running if there is no heating/cooling demand during occupied hours. So in this case, can you change the fan schedule to have the system only run when heating/cooling is required, not continuously during occupied hours as long as your natural ventilation is available? I'm assuming you can also set your Proposed HVAC outdoor air minimum to 0 since your are bringing in the outside air via natural ventilation, making it a return air only unit essentially.

Making this more complicated, if you're your natural ventilation system has a min or max outside air when it becomes unavailable, your HVAC system needs to become available with your minimum outdoor airflow to meet setpoint. It seems that this could possibly be done through the EMS or be done post process.

Does anyone have experience with this process or be able to provide any insight on my understanding of it?

How do I model natural ventilation for LEED in EnergyPlus?

I have come across a couple projects located in South America where they are looking to model natural ventilation as the only HVAC system for LEED. This is addressed in Appendix D of the Advanced Energy Modeling for LEED v2.1 document for those who have purchased it but I want to double check my interpretation and see if anyone has used this method.

My understanding in this situation is that the Proposed HVAC system should be the same as the Baseline HVAC system with the airflows and capacities being identical to account for when the natural ventilation system can't meet setpoint, whether the building is designed for this not. Since the natural ventilation is bringing in the required outside air, there is no reason for the Proposed HVAC system to be running if there is no heating/cooling demand during occupied hours. So in this case, can you change the fan schedule to have the system only run when heating/cooling is required, not continuously during occupied hours as long as your natural ventilation is available? I'm assuming you can also set your Proposed HVAC outdoor air minimum to 0 since your are bringing in the outside air via natural ventilation, making it a return air only unit essentially.

Making this more complicated, if your natural ventilation system has a min or max outside air when it becomes unavailable, your HVAC system needs to become available with your minimum outdoor airflow to meet setpoint. It seems that this could possibly be done through the EMS or be done post process.

Does anyone have experience with this process or be able to provide any insight on my understanding of it?