Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
0

IDF Setpoint Value

asked 2024-01-30 02:28:24 -0500

nisa's avatar

updated 2024-01-30 09:05:31 -0500

Hi everyone, In an IDF file's Schedule:Compact objects that has type "Temperature", what does the value of temperature setpoint mean? For example in a heating setpoint schedule if the setpoint is set to 24 degrees, does it mean that zone temperature will be set to 22 degrees or heating systems will start working when zone temperature hits 22? Sorry if this question sounds weird, I'm new to this.

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
0

answered 2024-01-30 09:02:40 -0500

A heating set point temperature of 24 C means there will be a heaing load in the zone if the zone temperature is predicted to be below 24 C without any HVAC. The HVAC system should turn on to provide heating and the zone should wind up at 24 C if there is sufficient heating capacity. It depends on the HVAC configuration whether the zone temperature will be at 24 C or near 24 C, or floating if there is no heating system.

edit flag offensive delete link more

Comments

As an addendum to this, note also that by default EnergyPlus's setpoints refer to the air temperature. This differs from a number of other simulation tools (e.g. Sunrel, AccuRate) which primarily use operative temperature (average of air and surface temperature).

Designbuilder provides a decent discussion of the issues here: https://designbuilder.co.uk/helpv7.0/Content/Calculation_Options.htm#Operativ

Jamie Sullivan's avatar Jamie Sullivan  ( 2024-01-31 16:24:29 -0500 )edit

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Training Workshops

Careers

Question Tools

1 follower

Stats

Asked: 2024-01-30 02:28:24 -0500

Seen: 42 times

Last updated: Jan 31