For V8.7.0, ZoneHVAC:LowTemperatureRadiant:VariableFlow
has an input field Heating Control Throttling Range. In your case, Temperature Control Type
should be MeanAirTemperature
, Heating Control Temperature Schedule
should be "20", and Heating Control Throttling Range
should be set to "2".
but in the first place, you should use the latest version of EnergyPlus. Old versions have so many bugs and lack many new features.
UPDATE
My answer above was wrong. Sorry about that. The setting above varies the hot water flow rate from 0kg/s at 21°C to the maximum flow rate at 19°C linearly.
Alternatively, you can use EMS to model a deadband. I modelled with an ExampleFile RadLoTempHydrCtrlOpt.idf (V9-4-0). The revised idf file is here.
The ExampleFile has 3 zones with ZoneHVAC:LowTemperatureRadiant:VariableFlow
. I added a simle code to override the heating setpoint for West Zone. Please find the following, especially EnergyManagementSystem:Program
.
Schedule:Compact,
RADIANT HEATING SETPOINTS, !- Name
TEMPERATURE, !- Schedule Type Limits Name
Through: 12/31, !- Field 1
For: Alldays, !- Field 2
Until: 24:00, !- Field 3
19; !- Field 4
ZoneHVAC:LowTemperatureRadiant:VariableFlow,
West Zone Radiant Floor, !- Name
RadiantSysAvailSched, !- Availability Schedule Name
West Zone, !- Zone Name
Zn001:Flr001, !- Surface Name or Radiant Surface Group Name
ConvectionOnly, !- Fluid to Radiant Surface Heat Transfer Model
0.012, !- Hydronic Tubing Inside Diameter {m}
0.016, !- Hydronic Tubing Outside Diameter {m}
autosize, !- Hydronic Tubing Length {m}
0.35, !- Hydronic Tubing Conductivity {W/m-K}
MeanAirTemperature, !- Temperature Control Type
ZeroFlowPower, !- Setpoint Control Type
HeatingDesignCapacity, !- Heating Design Capacity Method
Autosize, !- Heating Design Capacity {W}
, !- Heating Design Capacity Per Floor Area {W/m2}
, !- Fraction of Autosized Heating Design Capacity
0.00008, !- Maximum Hot Water Flow {m3/s}
West Zone Radiant Water Inlet Node, !- Heating Water Inlet Node Name
West Zone Radiant Water Outlet Node, !- Heating Water Outlet Node Name
0, !- Heating Control Throttling Range {deltaC}
Radiant Heating Setpoints, !- Heating Control Temperature Schedule Name
CoolingDesignCapacity, !- Cooling Design Capacity Method
Autosize, !- Cooling Design Capacity {W}
, !- Cooling Design Capacity Per Floor Area {W/m2}
, !- Fraction of Autosized Cooling Design Capacity
0.0012, !- Maximum Cold Water Flow {m3/s}
Zone 1 Cooling Water Inlet Node, !- Cooling Water Inlet Node Name
Zone 1 Cooling Water Outlet Node, !- Cooling Water Outlet Node Name
2.0, !- Cooling Control Throttling Range {deltaC}
Radiant Cooling Setpoints, !- Cooling Control Temperature Schedule Name
, !- Condensation Control Type
, !- Condensation Control Dewpoint Offset {C}
, !- Number of Circuits
; !- Circuit Length {m}
EnergyManagementSystem:Sensor,
MAT_West_Zone, !- Name
West Zone, !- Output:Variable or Output:Meter Index Key Name
Zone Mean Air Temperature; !- Output:Variable or Output:Meter Name
EnergyManagementSystem:Actuator,
Rad_Heating_SP, !- Name
RADIANT HEATING SETPOINTS, !- Actuated Component Unique Name
Schedule:Compact, !- Actuated Component Type
Schedule Value; !- Actuated Component Control Type
EnergyManagementSystem:ProgramCallingManager,
EMS_PCM_Rad_Heating_SP_Override, !- Name
InsideHVACSystemIterationLoop, !- EnergyPlus Model Calling Point
EMS_Program_Rad_Heating_SP_Override; !- Program Name 1
EnergyManagementSystem:Program,
EMS_Program_Rad_Heating_SP_Override, !- Name
IF MAT_West_Zone <= 19, !- Program Line 1
SET Rad_Heating_SP = 21, !- Program Line 2
ELSEIF MAT_West_Zone >= 21, !- A4
SET Rad_Heating_SP = 19, !- A5
ENDIF; !- A6
Output:EnergyManagementSystem,
Verbose, !- Actuator Availability Dictionary Reporting
Verbose, !- Internal Variable Availability Dictionary Reporting
ErrorsOnly; !- EMS Runtime Language ...