Minimum Heat Pump PLR in HVACTemplate:System:VRF is not changed

asked 2 years ago

Keigo's avatar

updated 2 years ago

A bug report.

No matter what value we enter in Minimum Heat Pump Part-Load Ratio in HVACTemplate:System:VRF, the generated expidf file always has Minimum Heat Pump Part-Load Ratio of 0.25 in AirConditioner:VariableRefrigerantFlow.

Preview: (hide)

1 Answer

Sort by » oldest newest most voted
1

answered 2 years ago

I am a bit surprised but yes the min PLR for the VRF HP is hard wired at 0.25. That should be fixed.

 CALL CreateNewObj('AirConditioner:VariableRefrigerantFlow')
 CALL AddToObjStr('Minimum Heat Pump Part-Load Ratio','0.25')
Preview: (hide)
link

Comments

Work around: place idf file in same folder as ExpandObjects.exe as in.idf. Double click ExpandObjects.exe. Rename expanded.idf to new file name. Edit new file and change VRF heat pump minimum part load ratio to desired value.

rraustad's avatar rraustad  ( 2 years ago )

Fixed for v23.1 in PR 9708.