First time here? Check out the Help page!

Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
1

Dehumidification (cool reheat) with chilled water (E+)

asked 2 years ago

Jim Dirkes's avatar

updated 2 years ago

I have never modeled a chilled water air handler system that uses the cool reheat strategy for dehumidification. I've tried a few approaches that are not controlling zone humidity. I've also looked for an example file which demonstrates that capability (and did not find one) What is needed to make that happen?

Preview: (hide)

1 Answer

Sort by » oldest newest most voted
1

answered 2 years ago

updated 2 years ago

This answer is a little old and OpenStudio-oriented, but I don't think any of the core info has changed.

A search of the example files folder for 'TemperatureAndHumidityRatio' returns a number of files with that input in the Controller:WaterCoil object, e.g.: 5ZoneWaterCooled_HighRHControl.idf, 5ZoneWaterCooled_MultizoneAverageRHControl.idf, 5ZoneWatercooled_MultizoneMinMaxRHControl.idf, to name a few.

Preview: (hide)
link

Comments

Spot on (for the controller and the example file). Thanks very much.

Jim Dirkes's avatar Jim Dirkes  ( 2 years ago )