Why Kiva results seems to reduce heat needs

asked 2022-04-04 12:07:07 -0500

cecile.cr's avatar

updated 2022-04-06 03:59:56 -0500

I model a single storey building with a big surface (15 744m²) heated to 15°C. The building has the following insulation: floor: 0.24 K.m²W-1; walls: 2.98 K.m²W-1; roof: 6.07K.m².W-1.

I use Kiva foundations with the following parameters:

Foundation:Kiva,
    Slab Details,             !- Name
    15,                       !- Initial Indoor Air Temperature
    ,                         !- Interior Horizontal Insulation Material Name
    ,                         !- Interior Horizontal Insulation Depth
    ,                         !- Interior Horizontal Insulation Width
    ,                         !- Interior Vertical Insulation Material Name
    ,                         !- Interior Vertical Insulation Depth
    ,                         !- Exterior Horizontal Insulation Material Name
    ,                         !- Exterior Horizontal Insulation Depth
    ,                         !- Exterior Horizontal Insulation Width
    ,                         !- Exterior Vertical Insulation Material Name
    ,                         !- Exterior Vertical Insulation Depth
    ,                         !- Wall Height Above Grade
    ,                         !- Wall Depth Below Slab
    ;                         !- Footing Wall Construction Name

Foundation:Kiva:Settings,
    1.8,                      !- Soil Conductivity
    3200,                     !- Soil Density
    836,                      !- Soil Specific Heat
    0.9,                      !- Ground Solar Absorptivity
    0.9,                      !- Ground Thermal Absorptivity
    0.03,                     !- Ground Surface Roughness
    40,                       !- FarField Width
    GroundWater,              !- DeepGround Boundary Condition
    10;                       !- DeepGround Depth


SurfaceProperty:ExposedFoundationPerimeter,
    PLANCHER +00_+00_+00,     !- Surface Name
    ExposedPerimeterFraction,    !- Exposed Perimeter Calculation Method
    ,                         !- Total Exposed Perimeter
    1,                        !- Exposed Perimeter Fraction
    ;                         !- Surface Segment 1 Exposed

The simulation gives 87MWh of heating over the whole year(ie. 5.4kWh/m²/year).

Secondly, I simulate the same building but with fixed ground temperature with the monthly median of the inside face temperature of the floor of the previous Kiva simulation (taken in the middle of the building). The simulation gives 100 MWh of heating over the whole year(ie. 6.35kWh/m²/year).

I expected the contrary because the second simulation takes the inside face temperature as the ground surface temperature (moreover on the center of the building floor). It seems that the comportement is worse when I use the procedure but with 18°C for the temperature set point.

Details: 192m x 82m (a surface of 15 744m²) with 3 meters of height. The building got 10 x 5 parts (19.2m x 8.2m each).

IDF and EPW:

https://drive.google.com/drive/folder...

Udated

It's like there is less exchanges when I use the Kiva model for the ground. Please look at the graph representing the floor surface conduction heat transfert: image description In the fixed ground temperature IDF there is to material layers for the floor: concrete + Insulation, but in the Kiva IDF I just put one layer with the insulation because the slab is already the concrete layer.

Finally, if I take the maximum of the "Surface Inside Face Temperature C" for each month in the Kiva solution for the second approach, results give me 83.5MWh. That's less than 2% above the Kiva solution.

edit retag flag offensive close merge delete

Comments

This is likely because Kiva uses ground temperatures that change each timestep instead of one average ground temperature used for an entire month. With the second approach, you miss the temperature fluctuations within each day.

Aaron Boranian's avatar Aaron Boranian  ( 2022-04-04 16:20:42 -0500 )edit

If I take the maximum of the "Surface Inside Face Temperature C" for each month in the Kiva solution for the second approach, results give me 83.5MWh. That's less than 2% above the Kiva solution... And it's the inside temperature, in the middle of the building.

cecile.cr's avatar cecile.cr  ( 2022-04-05 02:38:16 -0500 )edit
2

Can you see if using EnergyPlus 22.1 changes your results much? It includes two significant bugfixes for Kiva.

shorowit's avatar shorowit  ( 2022-04-06 08:54:06 -0500 )edit

Results changed a lot with this update, thank you for this advice! I wonder about this results: when I model the building in 50 blocks (10x5) (with really thin walls between each block), it gives 220MWh of heating needs over the year but when I model this same building with only 1 block it gives 144MWh. That's a 50% difference! (With the fixed temperature model the difference of heating needs between a one block building and a 50 blocks building is less than 6%).

cecile.cr's avatar cecile.cr  ( 2022-04-07 04:13:24 -0500 )edit

@cecile.cr it seems that you have made a new post for this new question regarding changing the number of floor surfaces impacting heating results. Is that correct?

Aaron Boranian's avatar Aaron Boranian  ( 2022-04-20 11:26:39 -0500 )edit

1 Answer

Sort by » oldest newest most voted
3

answered 2022-04-22 02:42:52 -0500

cecile.cr's avatar

Updating E+ to 22.1 seems to have fixed this bug. Thanks to @shorowit for this suggestion.

edit flag offensive delete link more

Comments

From what I know the issue was not fixed yet, so I don't understand why you say it is fixed in 22.1. Can you please provide the results and models? https://github.com/NREL/EnergyPlus/is...

Tokarzewski's avatar Tokarzewski  ( 2023-09-13 04:05:04 -0500 )edit

Updating E+ to 22.1 fixed this bug. After that, I created a new issue which is here : https://unmethours.com/question/72678.... This last question has more to do with the github problem you're pointing out.

cecile.cr's avatar cecile.cr  ( 2023-09-13 09:44:28 -0500 )edit