U-Value for Simple Glazing in OpenStudio Results

asked 2022-01-01 15:51:22 -0600

mattkoch's avatar

updated 2022-02-07 14:16:35 -0600

I am entering Simple Glazing with U-1.22, SHGC-0.25 and VT-0.275 for my window construction. The OpenStudio Results popping out in OpenStudio Application 1.2.1 report this with U-1.03, SHGC-0.25, VT-0.28, so the U-value is a bit off - and the VT-value rounded, I suppose. I reviewed https://bigladdersoftware.com/epx/doc... trying to understand why, but the approach discussed there (Rw = 1/U - Ri - Re) gives a Uw-value (1 over Rw-value) MUCH lower than even 1.03, so this 1.03 is probably not even the Uw-value. Any thoughts?

edit retag flag offensive close merge delete

2 Answers

Sort by » oldest newest most voted
5

answered 2022-01-02 15:30:54 -0600

updated 2022-01-03 10:40:10 -0600

image description

The linked screenshot compares OSApp v1.2.1 (SDK v321, E+ v9.5) vs v1.3.0 (SDK v330, E+ v9.6) input vs output (Benchmark Warehouse skylights, in SI units). I think this is simply linked to the following fix. From the E+ v9.6 Input Output Reference: "Field: U-Factor. ... In versions up till 9.6.0, the maximum allowable input is U-7.0 W/m2·K (~1.22), and the effective upper limit of the glazing generated by the underlying model is around U-5.8 W/m2·K (~1.03). In later versions, such upper bound of the input U value is removed. So is the mis-match between the user input U and the effective U is resolved."

edit flag offensive delete link more
2

answered 2022-01-01 18:11:08 -0600

saeranv's avatar

The Simple Glazing model uses a much more complex calculation to derive the window U-Value then Rw = 1/U - Ri - Re. It has to convert the U/SHGC/VT summary metrics into detailed window parameters representing an equivalent, feasible, single-layer window, so the derived summary metrics tend not to match inputs. The Simple Window documentation provides the details of the calculation.

edit flag offensive delete link more

Comments

Thank you. I am wondering then how the U-value from the OpenStudio Results report can be used to prove to USGBC/LEED that the window has indeed the U-1.22 it is supposed to have. I'd have to tell them that yes, it is entered as U-1.22, but due to internal calculations, EnergyPlus actually uses a different number?

mattkoch's avatar mattkoch  ( 2022-01-01 22:55:47 -0600 )edit

No, you'll have to find the detailed inputs for the actual window construction you're representing and build up a layer by layer detailed window assembly. So, assuming your getting the summary metrics from some window manafacturer, you just need to ask them for what the actual glass emittance/transmittance, conductivity etc. are. Then the calculated U-Value should match your target.

saeranv's avatar saeranv  ( 2022-01-02 01:23:37 -0600 )edit

I must admit I am confused. Are you referring to executing all the steps in the Simple Window documentation link you sent earlier? I can only see Step 1 effecting a re-computation of the U-Value, from U-value given (e.g. U-1.22) to glass resistance Rlw = 1/U - Riw - Row, which in turn may become its own U-value, namely Ulw = 1/Rlw? Or are you referring to using something like LBNL's WINDOW?

mattkoch's avatar mattkoch  ( 2022-01-02 13:47:53 -0600 )edit

I apologize, yes you're right. I thought there was a regression being done at some point but I must be confusing this with something. I think Denis has the right answer below.

saeranv's avatar saeranv  ( 2022-01-02 18:18:41 -0600 )edit