Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
2

ASHRAE90.1-2016, appendix-G, window U-value

asked 2019-06-17 14:55:06 -0500

updated 2019-06-17 17:55:17 -0500

Dear all, I have a question regarding how to generate the baseline window that required by ASHRAE90.1-2016 appendix-G.

The simple glazing method from Open Studio cannot give me a window with the U-value that in ASHRAE90.1 2016 appendix-G. I contacted the EnergyPlus help desk and have been told that it can be done by adding the frame.

Is there anyone please share a screenshot of the 2016 baseline model window's inputs (materials dataset and construction layer) for OpenStudio/EnergyPlus that you are using for climate zone 2?

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
1

answered 2019-06-20 08:47:05 -0500

The best approach is to describe the window in detail with built-up layers of materials and a frame so that they match the requirement in the standard. An alternative to that is to use WindowMaterial:SimpleGlazingSystem which uses an algorithm to create an equivalent single layer window. This algorithm is described in the engineering reference.

edit flag offensive delete link more

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Careers

Question Tools

1 follower

Stats

Asked: 2019-06-17 14:55:06 -0500

Seen: 365 times

Last updated: Jun 20 '19