Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
4

How to measure heating degree day (HDD) and cooling degree day (CDD) for a building

asked 2019-06-02 11:57:00 -0600

Md Jaynul Abden's avatar

updated 2019-06-12 09:20:18 -0600

I am not very much familiar with EnergyPlus simulation. Recently, I have developed a PCM based gypsum board for building envelope applications, i.e., wall, ceilings and floor. I also modeled a 4X4X3.5 m building room for measuring the indoor thermal environments, number of comfortable hours monthly/yearly with range 18 to 26 °C, HDD and CDD with and without use of my developed gypsum board in Wall and Ceiling. I can measure indoor temperature and energy consumption, but I cann't measure the comfortable hours, HDD and CDD.What's the output variable for these?

edit retag flag offensive close merge delete

3 Answers

Sort by » oldest newest most voted
5

answered 2019-06-07 08:40:20 -0600

Normally HDD and CDD are associated with a specific climate rather than to a particular building. ASHRAE 90.1 defines them as:

degree-day: the difference in temperature between the outdoor mean temperature over a twenty-four-hour period and a given base temperature.

In general, HDD and CDD are used as proxies to indicate much heating and cooling a typical building might have in different climates. It is a rough proxy since all buildings are different.

HDD is often at base 65F and CDD is at base 50F. The ASHRAE Handbook of Fundamentals (2017) contains Chapter 14 which describes this in more detail and has some example. For EnergyPlus weather files, the accompanying "stat" file contains information about HDD and CDD per month and annually.

edit flag offensive delete link more

Comments

Nice summary, but I have never seen a CDD base as low as 50F used. The CDD base is usually assumed to be either the same as the HDD base or typically higher. Having a CDD base lower than the HDD base implies a great deal of uncontrolled solar gains.

lirainer's avatar lirainer  ( 2019-06-10 10:36:20 -0600 )edit

@lirainer : I believe one major contextual reason for the CDD50 and HDD65 temperature conventions is that those are the average daily temperature bases used in definition of the climate zones. You'll find multiple sources tabulate CDD50/HDD65 side-by-side.

Nick Caton's avatar Nick Caton  ( 2019-06-11 19:34:33 -0600 )edit

@lirainer : For your 2nd assertion: For degree-day analyses, I have commonly encountered heating/cooling systems "overlap" in base temps, and 50/65 in isolation aren't totally weird... For example, bldgs in my climate have distinct heating/cooling seasons where boilers/chillers aren't needed at all for weeks at a time, but simultaneous operation is req'd in swing seasons. That equipment may be scheduled in a fashion correlative to avg OADB conditions. Knowing this, you'd want to select distinct base temperatures considering the OADB thresholds which bound heating/cooling loop operation.

Nick Caton's avatar Nick Caton  ( 2019-06-11 19:40:53 -0600 )edit
1

answered 2019-06-11 21:31:31 -0600

Nick Caton's avatar

If you are simply looking for degree day stats to fill in a box for something prescriptive like a LEED analysis, then Jason's response is almost certainly correct and you are then just simply looking to characterize the weather/climate for someone otherwise unfamiliar.

If however your specific phrasing "... for a building" infers that you are instead looking to practically apply a degree-day analysis to a specific building/climate/historical period... Awesome! I'll provide a response aimed at that sort of scenario.

Missing from the prompt is the point/purpose of such an analysis, which is important detail... So I'll provide some such context for sake of example. Let's assume you are performing a utility analysis for an existing facility, and after asserting a base:seasonal load split on your gas/electricity consumption history you are looking to evaluate the strength of a potential correlation between your seasonal energy consumption profiles and the corresponding degree days. The degree to which you can assert the "seasonal" energies align with CDD and HDD will lend confidence to your efforts and allow you to draw up a simple model correlating input weather conditions (in say, a TMY year) to estimate future projected baseline seasonal energy consumption, upon which you might be able to reasonably bound the potential savings associated with a boiler replacement.

To get there, we could just pull some CDD65 and/or HDD50 stats from a table, but those balance points might not be a good assumption for your specific situation. Let's describe our example further:
You know from an energy audit that seasonal gas usage is defined by only boiler consumption, which in turn service only a 2-pipe heating/cooling loop. The 2-pipe loop, as operated by the plant manager, is always in one of 3 states: heating, cooling, or inoperative. We can characterize the "inoperative" state as occurring generally in a temperature band around the building's balance point, where no substantial heating/cooling is necessary to maintain comfort. Never heating/cooling simultaneously. The BAS automated switchover is shot, but the plant operator does a good job of tracking occupant comfort and weather trends, and shared with us a historical log of dates the plant has been shifted between heating, cooling, and swing season states. Combining this data with historical AMY, we can ascertain that the boilers are characteristically in operation only when the daily average OADB is 57F or less. Further, the chillers are active only when daily average OADB is 66F or higher.

NOW we've established the most appropriate, building/climate/system-specific base temperatures upon which to base the stated degree day correllation study. One could alternatively avoid much of this field work and understanding in the systems' operations, having collected the historical weather and utility data, by simply interatively "backing into" a balance point which in turn produces a good fit, but you run the risk of missing any of these important details (like the deliberate non-operation of the plant ... (more)

edit flag offensive delete link more

Comments

Thanks Caton for your comments. I am not very much familiar with EnergyPlus simulation. Recently, I have developed a PCM based gypsum board for building envelope applications, i.e., wall, ceilings and floor. I also modeled a 4X4X3.5 m building room for measuring the indoor thermal environments, number of comfortable hours monthly/yearly with range 18 to 26 °C, HDD and CDD with and without use of my developed gypsum board in Wall and Ceiling. I can measure indoor temperature and energy consumption, but I cann't measure the comfortable hours, HDD and CDD.What's the output variable for these?

Md Jaynul Abden's avatar Md Jaynul Abden  ( 2019-06-12 09:18:43 -0600 )edit

I might clarify that heating/cooling degree days (HDD/CDD) to my experience are a metric used to characterize climate/weather conditions over time. Not occupant comfort. I too am inexperienced with e+, but am hopeful someone else more practiced might constructively step in to advise whatever output metrics exist natively for quantifying thermal comfort. If for example you were using a doe2/eQuest simulation, I would point you towards the standard SIM reports summarizing zonal temperatures through the simulation, or else the option to export interval measurements for further analysis.

Nick Caton's avatar Nick Caton  ( 2019-06-12 19:33:39 -0600 )edit
0

answered 2019-06-24 00:41:31 -0600

RicardoGallegos's avatar

updated 2019-06-24 00:48:44 -0600

Both HDD and CDD can be obtained via the "weather" utility in the EP Launch Utilities tab. You ask for a statistic report of your EPW filke, and he utility creates such a report. As for CDD and HDD, close to the end of the file you find these lines (taken from one of my local climate files, please note that formatting in this post is not exactly the one you get in the file):

  • Heating/Cooling Degree Days/Hours calculated from this weather file.
  • Heating/Cooling Degree Days/Hours from design conditions shown earlier in this report.
  • Monthly Weather File Heating/Cooling Degree Days/Hours

                             Jan   Feb  Mar Apr May Jun Jul Aug Sep Oct Nov Dec
    

    HDD base 10C 0 0 0 0 0 0 0 0 0 0 0 0
    HDD base 18C 87 39 10 0 0 0 0 0 0 9 51 99

    CDD base 10C 162 207 293 367 425 381 356 341 309 292 201 149
    CDD base 18C 1 21 55 127 177 141 108 93 70 53 12 0

    CDH base 20C 660 1062 1837 2885 3505 2610 1995 1745 1388 1427 849 574
    CDH base 23C 215 510 940 1759 2133 1392 879 715 514 666 318 199
    CDH base 27C 9 127 244 706 871 431 150 71 73 130 22 9

    • 3484 annual (wthr file) cooling degree-days (10°C baseline)
    • 0 annual (wthr file) heating degree-days (10°C baseline)

    • 858 annual (wthr file) cooling degree-days (18°C baseline)

    • 294 annual (wthr file) heating degree-days (18°C baseline)
edit flag offensive delete link more

Comments

Hi Ricardo, I have tried to calculate HDD and CDD according to your advise. It would be great if you please provide me EnergyPlus input file. My email is "mjaynul@gmail.com" Best Regards, Jaynul

Md Jaynul Abden's avatar Md Jaynul Abden  ( 2019-07-23 05:34:54 -0600 )edit

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Training Workshops

Careers

Question Tools

1 follower

Stats

Asked: 2019-06-02 11:57:00 -0600

Seen: 2,950 times

Last updated: Jun 24 '19