Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
1

Energy input ratio as a function of temperature curve output is not equal to 1.0

asked 6 years ago

l1023's avatar

updated 6 years ago

 ** Warning ** GetElectricEIRChillerInput: Chiller:Electric:EIR="MAIN CHILLER"
 **   ~~~   ** Energy input ratio as a function of temperature curve output is not equal to 1.0 (+ or - 10%) at reference conditions.
 **   ~~~   ** Curve output at reference conditions = 1.256
Preview: (hide)

1 Answer

Sort by » oldest newest most voted
2

answered 6 years ago

The curve that you are referencing in "Electric Input to Cooling Output Ratio Function of Temperature Curve Name" should be equal to 1 at the reference conditions set by "Reference Leaving Chilled Water Temperature" and "Reference Entering Condenser Fluid Temperature"