Energy input ratio as a function of temperature curve output is not equal to 1.0

asked 2019-01-28 04:23:01 -0600

l1023's avatar

updated 2019-01-28 10:33:19 -0600

 ** Warning ** GetElectricEIRChillerInput: Chiller:Electric:EIR="MAIN CHILLER"
 **   ~~~   ** Energy input ratio as a function of temperature curve output is not equal to 1.0 (+ or - 10%) at reference conditions.
 **   ~~~   ** Curve output at reference conditions = 1.256
edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
2

answered 2019-01-28 07:46:45 -0600

The curve that you are referencing in "Electric Input to Cooling Output Ratio Function of Temperature Curve Name" should be equal to 1 at the reference conditions set by "Reference Leaving Chilled Water Temperature" and "Reference Entering Condenser Fluid Temperature"