Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
1

Energy input ratio as a function of temperature curve output is not equal to 1.0

asked 2019-01-28 04:23:01 -0500

l1023's avatar

updated 2019-01-28 10:33:19 -0500

 ** Warning ** GetElectricEIRChillerInput: Chiller:Electric:EIR="MAIN CHILLER"
 **   ~~~   ** Energy input ratio as a function of temperature curve output is not equal to 1.0 (+ or - 10%) at reference conditions.
 **   ~~~   ** Curve output at reference conditions = 1.256
edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
2

answered 2019-01-28 07:46:45 -0500

The curve that you are referencing in "Electric Input to Cooling Output Ratio Function of Temperature Curve Name" should be equal to 1 at the reference conditions set by "Reference Leaving Chilled Water Temperature" and "Reference Entering Condenser Fluid Temperature"

To learn more, please read the InputOutputReference for the Chiller:Electric:EIR object.

edit flag offensive delete link more

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Careers

Question Tools

1 follower

Stats

Asked: 2019-01-28 04:23:01 -0500

Seen: 237 times

Last updated: Jan 28 '19