Do you know if there is any component available in the BUILDINGS library in Modelica, to operate windows (open or close) according to the outside conditions? I am looking at an exercise where I will model a house, and based on the outside condition I will operate in natural or mechanical mode. I know that this can be implemented by coupling EnergyPlus and modelica, but I am interested in using Modelica solely.

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
5

answered 2017-06-07 07:39:44 -0600

The opening/closing part can be implemented with blocks from the Modelica Standard Library. What is missing is a model that computes ventilation through an open window based on the window opening, wind speed and possibly temperature differential between room and outside. If you have such a correlation that is applicable for your building, you could implement it in a block and then prescribe this inflowing or outflowing mass flow rate between the outside and the room model.

edit flag offensive delete link more

Comments

Thank you for the very quick reply! I will try to use blocks then.

Charalampos Angelopoulos's avatar Charalampos Angelopoulos  ( 2017-06-07 07:45:12 -0600 )edit

@Charalampos Angelopoulos: if this solved your problem, please mark the answer as accepted (check mark next to it that will turn green) so that we can flag the question as resolved. Thanks!

Julien Marrec's avatar Julien Marrec  ( 2017-06-09 03:45:29 -0600 )edit

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Training Workshops

Careers

Question Tools

1 follower

Stats

Asked: 2017-06-07 05:27:15 -0600

Seen: 248 times

Last updated: Jun 09 '17