Define machines which produce heat
Hello i defined a few machines which produce heat, which is given into the zone. Therefore i Defined the Field. Fraction Lost with 0.5 so half of the energy will be give to the room. I expected that i will than have lesser gas consumption for the zone, but the opposites happens. When i place more and more electric equipment into the zone, the Gas Consumption increase
when i increase the Desing Level from my electric equipment form for example 200 to 8000 that i need more gas for heating than before. i have fraction at 0.5 so half of the heat from my machines goes into the room the rest i used for mechanical work
This is the reverse of what one would expect. We will need more info about the model, including the type of hvac system, to figure out why. Probably easiest if you post your idf file.
it is a HVAC Systm with Cooling with electricity and heating with gas. When i put i machines the cooling in summer increases but in the winter time i have got a higher gas Consumption when i put in machines. so the influence of the machines in summer is right and seemed logic to me, but not in the winter. i ve go 23 degrees air temperatured defined for the zones.
which part of the idf file do u need?
@Marcelba First, try to diagnose it yourself. Add some hourly output:variables that show what is happening in the zone heat balance, internal gains, and the hvac system. If you still have questions, then we need to see the complete idf file. And specify what epw file you are running with. If you prefer not to post that publicly, then you can send it to the EnergyPlus helpdesk at EnergyPlus_Support@gard.com