Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
4

Cooling Tower is storing excess heat the majority of the time

asked 2017-03-20 20:22:23 -0600

katsuya.obara's avatar

I have problem for modeling in water side.
Chiller COP is lower than 1 for all the time. Investigating the result, seems that condenser outlet and inlet temperature from chiller is so high (Inlet:53degC - 75degC, Outlet:58degC - 80degC) as shown in histogram below.
Then looking at the err file, found that Plant Loop: SD1 CW LOOP Demand Side is storing excess heat the majority of the time. Plant Loop: SD1 CW LOOP Supply Side is storing excess heat the majority of the time.enter code here
Does anyone know what is causing this warning and how I can fix this problem?

image description

edit retag flag offensive close merge delete

Comments

Did you figure out the issue?

rkbest's avatar rkbest  ( 2018-05-01 14:32:34 -0600 )edit

Is the issue resolved ?

Siv's avatar Siv  ( 2018-09-26 23:02:26 -0600 )edit

1 Answer

Sort by ยป oldest newest most voted
0

answered 2018-08-23 14:38:12 -0600

taher.ahel's avatar

I've had the same problem with my heating loop. I Set the PlantLoop: Plant Loop Demand Calculation Scheme temperature setpoint to my loop design temperature and it get solve. I mean I'd set this setpoint at 60 deg and my boiler had been set on 82 deg. so I changed PlantLoop: Plant Loop Demand Calculation Scheme setpoint to 82 deg and it get solve.

edit flag offensive delete link more

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Training Workshops

Careers

Question Tools

1 follower

Stats

Asked: 2017-03-20 20:22:23 -0600

Seen: 529 times

Last updated: Aug 23 '18