Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
3

HVAC Ratings: SEER for 8 TR and more heat pumps?

asked 2017-03-05 11:33:41 -0500

rkbest's avatar

updated 2017-04-27 08:27:54 -0500

Recently I was told not to use SEER/EER ratings for heat-pumps of 8 TR capacity (or more) and to check when the rating can be used and not. I am unable to find any literature which suggests the limitation of using terms SEER and EER rating with capacity. Any insights on this topic?

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
3

answered 2017-03-06 12:13:47 -0500

AHRI Standard 210/240 uses SEER as the performance rating metric for air-cooled heat pumps up to 65,000 Btu/h (~5.4 tons).

AHRI Standard 340/360 uses EER as the (full-load) performance rating metric for air-cooled heat pumps up to 250,000 Btu/h (~20 tons).

EER is also used for water-source heat pump cooling efficiency as defined in ISO 13256-1 and 13256-2.

edit flag offensive delete link more

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Careers

Question Tools

1 follower

Stats

Asked: 2017-03-05 11:33:41 -0500

Seen: 199 times

Last updated: Mar 06 '17