Is possible to calculate the heating rate using COMPACT HVAC:ZONE:PURCHASED AIR in Energy Plus v. 8.6?

asked 2017-02-17 23:13:37 -0600

melanie's avatar

updated 2017-02-17 23:14:12 -0600

I'm trying to calculate the heating rate. The InputOutputReference of 2008 and others documents suggest to use the COMPACT HVAC:ZONE:PURCHASED AIR. But I'm using the version 8.6 of Energy Plus and can't find that class. There is something equivalent in the version 8.6?

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
3

answered 2017-02-20 15:37:30 -0600

Ricardo GAllegos's avatar

updated 2017-02-21 05:36:00 -0600

Ideal Load Air System is a concept totally equivalent to purchased air. Check the input output reference manual. You can use the HVACTemplate objects for convenience:

Or the ZoneHVAC:IdealLoadsAirSystem directly.

edit flag offensive delete link more

Comments

I took the liberty of adding links to the documentation and mention the non HVACTemplate option.

Worth reading the first paragraph here:

The simplest way to add HVAC control to an EnergyPlus thermal zone is to use the ZoneHVAC:IdealLoadsAirSystem. This was called purchased air in older versions

Julien Marrec's avatar Julien Marrec  ( 2017-02-21 05:36:21 -0600 )edit