Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
2

Is possible to calculate the heating rate using COMPACT HVAC:ZONE:PURCHASED AIR in Energy Plus v. 8.6?

asked 2017-02-17 23:13:37 -0500

melanie's avatar

updated 2017-02-17 23:14:12 -0500

I'm trying to calculate the heating rate. The InputOutputReference of 2008 and others documents suggest to use the COMPACT HVAC:ZONE:PURCHASED AIR. But I'm using the version 8.6 of Energy Plus and can't find that class. There is something equivalent in the version 8.6?

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
3

answered 2017-02-20 15:37:30 -0500

Ricardo GAllegos's avatar

updated 2017-02-21 05:36:00 -0500

Ideal Load Air System is a concept totally equivalent to purchased air. Check the input output reference manual. You can use the HVACTemplate objects for convenience:

Or the ZoneHVAC:IdealLoadsAirSystem directly.

edit flag offensive delete link more

Comments

I took the liberty of adding links to the documentation and mention the non HVACTemplate option.

Worth reading the first paragraph here:

The simplest way to add HVAC control to an EnergyPlus thermal zone is to use the ZoneHVAC:IdealLoadsAirSystem. This was called purchased air in older versions

Julien Marrec's avatar Julien Marrec  ( 2017-02-21 05:36:21 -0500 )edit

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Careers

Question Tools

1 follower

Stats

Asked: 2017-02-17 23:13:37 -0500

Seen: 123 times

Last updated: Feb 21 '17