Where can I read the Outdoor Air flow per Zone in CFM ou m³/h?

In Outdoor Air Summary - EnergyPlus report we can see only the Zone Volume and Mechanical Ventilation, but the Flow is not showed. Is there some another report to show this?

edit retag flag offensive close merge delete

1 Answer

Sort by » oldest newest most voted
3

answered 2016-09-28 06:57:46 -0600

In the tabular reports, I would start by looking at the Standard 62.1 Summary which will show for each system the Outdoor Air Intake Flow - Vot for heating and cooling and for each zone the need for outdoor air.

Outdoor air is also shown in the tabular reports in the Component Sizing Summary report under Controller:OutdoorAir and it will show the minimum and maximum (using economizer) outdoor air flow in m3/s or CFM for each system.

The use of SI or IP units can be set in the OutputControl:Table:Style object.

edit flag offensive delete link more

Comments

@JasonGlazer I don't know why, but this report Component Sizing Summary - Controller Outdoor Air not are showing in this model specific. In another models is common that ar showed only some Air Loops, while other are not showed.

Geraldo Pithon's avatar Geraldo Pithon  ( 2016-09-28 11:41:03 -0600 )edit

You probably don't have a Controller:OutdoorAir object that is getting autosized.

JasonGlazer's avatar JasonGlazer  ( 2016-09-28 12:15:14 -0600 )edit

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Training Workshops

Careers

Question Tools

1 follower

Stats

Asked: 2016-09-27 15:09:21 -0600

Seen: 183 times

Last updated: Sep 28 '16