Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
2

VRF condenser type report

asked 2016-01-27 12:38:16 -0500

ngkhanh's avatar

updated 2016-02-01 01:35:38 -0500

It seems the condenser type of VRF system in E+ Component Sizing Report is evaporative even we setup as air cooled in idf file.

Please someone check and confirm about this problem.

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
3

answered 2016-01-27 18:36:17 -0500

updated 2016-02-01 01:35:09 -0500

I ran the VariableRefrigerantFlow_5Zone example file and also changed the condenser type to EvaporativelyCooled. The results shown in the Component Sizing Summary using V8.4 appear correct.

The first table denotes the air-cooled simulation while the second table reflects the results of the evap-cooled simulation. The results show the values for autosized input fields.

Top one is air cooled, bottom is evaporatively cooled

edit flag offensive delete link more

Comments

2 tables for difference selection ? i can only get 1 table not both

ngkhanh's avatar ngkhanh  ( 2016-01-28 08:27:33 -0500 )edit

I pasted the tables from 2 simulations into a single picture so you could see them both at once. The top table is air-cooled, the bottom table is evaporatively-cooled.

rraustad's avatar rraustad  ( 2016-01-28 08:47:02 -0500 )edit

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Training Workshops

Careers

Question Tools

1 follower

Stats

Asked: 2016-01-27 12:38:16 -0500

Seen: 150 times

Last updated: Feb 01 '16