Location of Preheat coil

asked 2026-02-12 21:47:58 -0500

Keigo's avatar

I'd like to confirm the location of a preheat coil which is required for ASHRAE PRM Baseline Systems 5 through 8 as per 90.1-2016 G3.1.3.19, 90.1-2019 G3.1.3.19 and 90.1-2022 G3.2.3.19.

image description

ASHRAE 90.1 and ASHRAE 90.1 User's Manual do not explicitly state the location of the preheat coil.

PNNL's Reference Manual suggests that the preheat coil shall be located in the mixed air stream i.e. after the outdoor air and return air are mixed, but I don't fully trust the refernce manual. It sometimes makes mistakes. image description

In the EnergyPlus documentation, "preheat" refers to heating the outdoor air. A preheat coil is located in the outdoor air stream.

Which location is correct for ASHRAE 90.1 PRM? Any source? Just an opinion would be appreciated.

image description

edit retag flag offensive close merge delete

4 Answers

Sort by » oldest newest most voted
3

answered 2026-04-15 09:35:28 -0500

I would say the preheat coil is intended to be in the mixed air stream, like the PNNL reference manual suggested. Generally, the purpose of the preheat coil is to temper the air before it enters the cooling coil, and you might as well mix the return air first, since that is going to be warmer.

If you really want to waste energy, you could locate the preheat coil a few feet before the outdoor air intake :-)

edit flag offensive delete link more
1

answered 2026-04-15 11:13:36 -0500

updated 2026-04-22 08:43:45 -0500

If located in the OA stream, you would get a higher LMTD heat transfer efficiency and will need a smaller coil (due to higher deltaT).

For the return air stream option, if the return air is picking up moisture from the space and if the OA temperature is low, might get condensation in the mixing box,.

And if the AHU has a heat recovery coil. it defenately has to be in the OA stream to prevent freezing of the heat recovery coil

edit flag offensive delete link more

Comments

This is a baseline case. It does not have a heat recovery coil.

Keigo's avatar Keigo  ( 2026-04-22 21:48:38 -0500 )edit
0

answered 2026-04-14 21:49:26 -0500

I would say the mixed air stream. I don't have a source to point to, but why not take advantage of RA mixing/preheating before heating mechanically?

edit flag offensive delete link more

Comments

Thanks for your opinion. This is a requirement for the baseline case. We are happy when the baseline case consumes more energy i.e., happy if the preheat coil can be located in the OA stream.

Keigo's avatar Keigo  ( 2026-04-14 22:01:52 -0500 )edit

I was just speaking from a design perspective. I think there'd only be a preheat coil before the mixing box for frost control with exhaust air heat recovery. The Engineering Reference (16.8.1.4) says: "The preheat coil should be controlled to maintain a minimum supply air inlet temperature thereby eliminating frost buildup on the heat exchanger core." My interpretation would be one preheat coil to bring the OA up to 35F, then another preheat coil to bring the MA up to 20F below heating setpoint.

I agree the location(s) should be stated explicitly in 90.1.

ericmartinpe's avatar ericmartinpe  ( 2026-04-15 07:57:34 -0500 )edit
0

answered 2026-04-14 08:02:53 -0500

If there is no heat exchanger, then I don't think it matters where this preheat coil is located in terms of energy usage. The load will be the same regardless. It will either be small flow rate with large delta T, if only outdoor air, or higher flow rate with smaller delta T in a mixed air configuration. In both configurations above (assuming that is no heat exchanger) the load on the coil is basically the same. If you are following the PNNL document above then it should be in the mixed air stream. In real life I would expect it to be in the OA stream, but, importantly, Appendix G systems aren't real life. I would place it in the space where it is with the system you are comparing it with. If you aren't comparing it with another system I would refer back to how much energy is it actually using? It will be pretty much the same in either configuration.

edit flag offensive delete link more

Comments

Say, OA is 0ºC (32ºF), and the indoor heating setpoint is 20ºC (68ºF). The preheat coil heats the air up to 9ºC (48ºF). If the preheat coil is located in the OA stream, the coil operates. If the coil is located in the mixed air stream, the mixed air temperature is the mixture of OA (0ºC (32ºF)) and RA (20ºC (68ºF)), which can be above 9ºC (48ºF), and the coil would not operate. That happened in my baseline case. The location matters.

Keigo's avatar Keigo  ( 2026-04-14 09:50:48 -0500 )edit

Excellent point. I would say in most VAV systems this would happen (the temperature after the mixer would be above 9'C), as the return air flow from the zones is preheating the total air flow going to the AHU coils. The main thing is deciding what the purpose of the preheat coil is. I would always go back to the configuration of the system you are comparing with and put it in the same position, or if you aren't comparing it look at its purpose (is it to ensure the components in the air handling units don't freeze?) and put it in the correct position.

Annie Marston's avatar Annie Marston  ( 2026-04-14 12:21:10 -0500 )edit

I would just like to know the correct interpretation of ASHRAE 90.1 Appendix G. Preheat coil is required in the baseline systems 5 through 8 even if the proposed case does not have it.