I gave it the exact same title as this old post. It seems that AirTerminal:SingleDuct:VAV:Reheat
and AirTerminal:SingleDuct:VAV:HeatAndCool:Reheat
have not changed that much since 8 years ago, but I'm not satisfied with the answer in the old post. To be more precise, I want to clarify the difference between AirTerminal:SingleDuct:VAV:Reheat
with Reverse
damper heating action and AirTerminal:SingleDuct:VAV:HeatAndCool:Reheat
.
For AirTerminal:SingleDuct:VAV:Reheat
, the Reverse
damper heating action is also called the dual maximum control logic as illustrated in the following figure.
For AirTerminal:SingleDuct:VAV:HeatAndCool:Reheat
, @Adam Hilton, the questioner of the old post interpreted Input/Output Reference as follows:
VAV:HeatAndCool:Reheat
increases the air flow to maximum first, then modulates the reheat valve to 100%.
This is incorrect, at least according to simulation results. When the heating load is small enough to handle with the Mnimum Air Flow Fraction
, the airflow starts from the Mnimum Air Flow Fraction
, and the supply air temperature is gradually increased. The aiflow increases only after the heating load increases and the supply air temperature reaches the Maximum Reheat Air Temperature
, which is the same as the figure above! If this simulation result is not as intended for AirTerminal:SingleDuct:VAV:HeatAndCool:Reheat
, this should be a bug.
I don't know the difference between AirTerminal:SingleDuct:VAV:Reheat
with Reverse
damper heating action and AirTerminal:SingleDuct:VAV:HeatAndCool:Reheat
. Both have Mnimum Air Flow Fraction
and Maximum Reheat Air Temperature
. When the heating load increases, both start with Mnimum Air Flow Fraction
and both increase airflow after the supply air temperature reaches Maximum Reheat Air Temperature
.
Actually, the simulation results of AirTerminal:SingleDuct:VAV:Reheat
with Reverse
damper heating action and AirTerminal:SingleDuct:VAV:HeatAndCool:Reheat
are not exactly the same, but their control logic looks very similar.
Could someone (or @rraustad) clarify the difference between AirTerminal:SingleDuct:VAV:Reheat
with Reverse
damper heating action and AirTerminal:SingleDuct:VAV:HeatAndCool:Reheat
? I would appreciate it even more if you could illustrate it. The problem is that Input/Output Reference does not illustrate the control logic of AirTerminal:SingleDuct:VAV:HeatAndCool:Reheat