AirLoopHVAC Autosizing does not recognise load from ZoneHVAC:OutdoorAirUnit

A bug report. As per the title. A sample idf file is here (V22-2-0). It's based on the ExampleFile: OutdoorAirUnitwithAirloopHVAC.idf, but I revised it a little bit. There are 5 conditioned zones in the ExampleFile, and only SPACE4-1 has both ZoneHVAC:OutdoorAirUnit and AirLoopHVAC. Originally, ZoneHVAC:OutdoorAirUnit for SPACE4-1 has HeatExchanger:AirToAir:Plate and Coil:Cooling:Water, but I removed them, which is irrerevant to the bug I want to report. Below is the air-side schematic. Please imagine that a kitchen has VAV system + Fresh air makeup fan with preheat coil. I want to model that kind of system. So, the ZoneHVAC:OutdoorAirUnit here is meant to be Fresh air makeup fan with preheat coil.

image description

AirLoopHVAC VAV Sys 4-1 and AirTerminal:Singleduct:VAV:Reheat are autosized, but it seems that they do not recognise the fresh air load from ZoneHVAC:OutdoorAirUnit, which results in so many unmet hours in the annual run.

Some notes:

  • The sequence described in ZoneHVAC:EquipmentList is ZoneHVAC:OutdoorAirUnit first and ZoneHVAC:AirDistributionUnit second.
  • I tried chaning Account for Dedicated Outdoor Air System in Sizing:Zone from "No" to "Yes", but in vein.
  • I tried modelling "Fresh air makeup fan with preheat coil" with AirLoopHVAC instead of ZoneHVAC:OutdoorAirUnit i.e. there are two AirLoops in one zone. EnergyPlus allows two AirLoops in one zone, but autosizing does not work well. Tthe VAV system (one AirLoopHVAC) also did not recognise the fresh air load from Fresh air makeup fan with preheat (another AirLoopHVAC) during sizing run. I will report this as a separate post later.

Is there any way to make AirLoopHVAC recognise the load fromZoneHVAC:OutdoorAirUnit?

AirLoopHVAC Autosizing does not recognise load from ZoneHVAC:OutdoorAirUnit

A bug report. As per the title. A sample idf file is here (V22-2-0). It's based on the ExampleFile: OutdoorAirUnitwithAirloopHVAC.idf, but I revised it a little bit. There are 5 conditioned zones in the ExampleFile, and only SPACE4-1 has both ZoneHVAC:OutdoorAirUnit and AirLoopHVAC. Originally, ZoneHVAC:OutdoorAirUnit for SPACE4-1 has HeatExchanger:AirToAir:Plate and Coil:Cooling:Water, but I removed them, which is irrerevant to the bug I want to report. Below is the air-side schematic. Please imagine that a kitchen has VAV system + system, Exhaust fan and Fresh air makeup fan with preheat coil. I want to model that kind of system. So, the ZoneHVAC:OutdoorAirUnit here is meant to be Exhaust fan and Fresh air makeup fan with preheat coil.

image descriptionimage description

AirLoopHVAC VAV Sys 4-1 and AirTerminal:Singleduct:VAV:Reheat are autosized, but it seems that they do not recognise the fresh air load from ZoneHVAC:OutdoorAirUnit, which results in so many unmet hours in the annual run.

Some notes:

  • The sequence described in ZoneHVAC:EquipmentList is ZoneHVAC:OutdoorAirUnit first and ZoneHVAC:AirDistributionUnit second.
  • I tried chaning Account for Dedicated Outdoor Air System in Sizing:Zone from "No" to "Yes", but in vein.
  • I tried modelling "Fresh "Exhaust fan and Fresh air makeup fan with preheat coil" with AirLoopHVAC instead of ZoneHVAC:OutdoorAirUnit i.e. there are two AirLoops in one zone. EnergyPlus allows two AirLoops in one zone, but autosizing does not work well. Tthe The VAV system (one AirLoopHVAC) also did not recognise the fresh air load from the Fresh air makeup fan with preheat (another AirLoopHVAC) during sizing run. I will report this as a separate post later.when I have time.

Is there any way to make AirLoopHVAC recognise the load fromZoneHVAC:OutdoorAirUnit?

AirLoopHVAC Autosizing does not recognise load from ZoneHVAC:OutdoorAirUnit

A bug report. As per the title. A sample idf file is here (V22-2-0). It's based on the ExampleFile: OutdoorAirUnitwithAirloopHVAC.idf, but I revised it a little bit. There are 5 conditioned zones in the ExampleFile, and only SPACE4-1 has both ZoneHVAC:OutdoorAirUnit and AirLoopHVAC. Originally, ZoneHVAC:OutdoorAirUnit for SPACE4-1 has HeatExchanger:AirToAir:Plate and Coil:Cooling:Water, but I removed them, which is irrerevant to the bug I want to report. Below is the air-side schematic. Please imagine that a kitchen has VAV system, Exhaust fan and Fresh air makeup fan with preheat coil. I want to model that kind of system. So, the ZoneHVAC:OutdoorAirUnit here is meant to be Exhaust fan and Fresh air makeup fan with preheat coil.

image description

AirLoopHVAC VAV Sys 4-1 and AirTerminal:Singleduct:VAV:Reheat are autosized, but it seems that they do not recognise the fresh air load from ZoneHVAC:OutdoorAirUnit, which results in so many unmet hours in the annual run.

Some notes:

  • The sequence described in ZoneHVAC:EquipmentList is ZoneHVAC:OutdoorAirUnit first and ZoneHVAC:AirDistributionUnit second.
  • I tried chaning Account for Dedicated Outdoor Air System in Sizing:Zone from "No" to "Yes", but in vein.
  • I tried modelling "Exhaust fan and Fresh air makeup fan with preheat coil" with AirLoopHVAC instead of ZoneHVAC:OutdoorAirUnit i.e. there are two AirLoops in one zone. EnergyPlus allows two AirLoops in one zone, but autosizing does not work well. The VAV system (one AirLoopHVAC) also did not recognise the fresh air load from the Fresh air makeup fan with preheat (another AirLoopHVAC) during sizing run. I will report this as a separate post when I have time.

Is there any way to make AirLoopHVAC recognise the load fromZoneHVAC:OutdoorAirUnit?

AirLoopHVAC Autosizing does not recognise load from ZoneHVAC:OutdoorAirUnit

A bug report. As per the title. A sample idf file is here (V22-2-0). It's based on the ExampleFile: OutdoorAirUnitwithAirloopHVAC.idf, but I revised it a little bit. There are 5 conditioned zones in the ExampleFile, and only SPACE4-1 has both ZoneHVAC:OutdoorAirUnit and AirLoopHVAC. Originally, ZoneHVAC:OutdoorAirUnit for SPACE4-1 has HeatExchanger:AirToAir:Plate and Coil:Cooling:Water, but I removed them, which is irrerevant to the bug I want to report. Below is the air-side schematic. Please imagine that a kitchen has VAV system, Exhaust fan and Fresh air makeup fan with preheat coil. I want to model that kind of system. So, the ZoneHVAC:OutdoorAirUnit here is meant to be Exhaust fan and Fresh air makeup fan with preheat coil.

image description

AirLoopHVAC VAV Sys 4-1 and AirTerminal:Singleduct:VAV:Reheat are autosized, but it seems that they do not recognise the fresh air load from ZoneHVAC:OutdoorAirUnit, which results in so many unmet hours in the annual run.

Some notes:

  • The sequence described in ZoneHVAC:EquipmentList is ZoneHVAC:OutdoorAirUnit first and ZoneHVAC:AirDistributionUnit second.
  • I tried chaning Account for Dedicated Outdoor Air System in Sizing:Zone from "No" to "Yes", but in vein.
  • I tried modelling "Exhaust fan and Fresh air makeup fan with preheat coil" with AirLoopHVAC instead of ZoneHVAC:OutdoorAirUnit i.e. there are two AirLoops in one zone. EnergyPlus allows two AirLoops in one zone, but autosizing does not work well. The VAV system (one AirLoopHVAC) also did not recognise the fresh air load from the Fresh air makeup fan with preheat (another AirLoopHVAC) during sizing run. I will report this as a separate post when I have time.
  • ZoneVentilation:DesignFlowRate is not appropriate because I need to model a preheat coil on the fresh air makeup.

Is there any way to make AirLoopHVAC recognise the load fromZoneHVAC:OutdoorAirUnit?

AirLoopHVAC Autosizing does not recognise load from ZoneHVAC:OutdoorAirUnit

A bug report. As per the title. A sample idf file is here (V22-2-0). It's based on the ExampleFile: OutdoorAirUnitwithAirloopHVAC.idf, but I revised it a little bit. There are 5 conditioned zones in the ExampleFile, and only SPACE4-1 has both ZoneHVAC:OutdoorAirUnit and AirLoopHVAC. Originally, ZoneHVAC:OutdoorAirUnit for SPACE4-1 has HeatExchanger:AirToAir:Plate and Coil:Cooling:Water, but I removed them, which is irrerevant to the bug I want to report. Below is the air-side schematic. Please imagine that a kitchen has VAV system, Exhaust fan and Fresh air makeup fan with preheat coil. I want to model that kind of system. So, the ZoneHVAC:OutdoorAirUnit here is meant to be Exhaust fan and Fresh air makeup fan with preheat coil.

image descriptionimage description

AirLoopHVAC VAV Sys 4-1 and AirTerminal:Singleduct:VAV:Reheat are autosized, but it seems that they do not recognise the fresh air load from ZoneHVAC:OutdoorAirUnit, which results in so many unmet hours in the annual run.

Some notes:

  • The sequence described in ZoneHVAC:EquipmentList is ZoneHVAC:OutdoorAirUnit first and ZoneHVAC:AirDistributionUnit second.
  • I tried chaning Account for Dedicated Outdoor Air System in Sizing:Zone from "No" to "Yes", but in vein.
  • I tried modelling "Exhaust fan and Fresh air makeup fan with preheat coil" with AirLoopHVAC instead of ZoneHVAC:OutdoorAirUnit i.e. there are two AirLoops in one zone. EnergyPlus allows two AirLoops in one zone, but autosizing does not work well. The VAV system (one AirLoopHVAC) also did not recognise the fresh air load from the Fresh air makeup fan with preheat (another AirLoopHVAC) during sizing run. I will report this as a separate post when I have time.
  • ZoneVentilation:DesignFlowRate is not appropriate because I need to model a preheat coil on the fresh air makeup.

Is there any way to make AirLoopHVAC recognise the load fromZoneHVAC:OutdoorAirUnit?