Chiller is ON but Cooling Tower is OFF

I got stuck over the weird behavior of my model. My model is a small office building with the following chilled water loop and condenser water loops.

image description

I bullet-point the situation.

  • The problem is that cooling towers and condenser pumps are off even when there is a cooling demand on the chilled water loop and the chiller is operating. The annual end use of Pumps and Heat Rejection is extremely small.
  • The problem occurred after I changed Pump Control Type from Continuous to Intermittent.
  • When there is a cooling demand on the chilled water loop, a cooling demand on the condenser water loop is 0.
  • There is a lot of Chiller Condenser Heat Transfer even though the condenser pumps and cooling towers are off, which makes no sense.
  • Chillers cool the chilled water even though the condenser loop is off.
  • Chiller Condenser Inlet Temperature is constant throughout the year (25.74°C for Chiller1 and 25.84°C for Chiller2), which is the weirdest thing in my model. Chillers cool chilled water without running cooling towers probably due to this constant condenser inlet temperature, but I don't know why the temperature at this node is constant.
  • Unmet hours are not detected even though the condenser loop is off.
  • Free convection in CoolingTower:TwoSpeed is not modelld.
  • Plant Loop Volume is autosized. I hardsized it to 0m3 as a trial, but the problem was not solved.

The charts below are one-week extracts of the simulation results in summer.

Cooling towers and condenser pumps are off.

image description

Chiller Condenser Inlet Temperature and Cooling Tower Outlet Temperature do not match at all.

image description

I have put the idf files here. Their version is V9-6-0. The model with continuous pumps is just for comparision.

I have modelled similar systems several times before, but this is the first time I have this problem. Any suggestion for solving this problem would be appreciated.

Chiller is ON but Cooling Tower is OFF

I got stuck over the weird behavior of my model. My model is a small office building with the following chilled water loop and condenser water loops.

image description

I bullet-point the situation.

  • The problem is that cooling towers and condenser pumps are off even when there is a cooling demand on the chilled water loop and the chiller is operating. The annual end use of Pumps and Heat Rejection is extremely small.
  • The problem occurred after I changed Pump Control Type from Continuous to Intermittent.
  • When there is a cooling demand on the chilled water loop, a cooling demand on the condenser water loop is 0.
  • There is a lot of Chiller Condenser Heat Transfer even though the condenser pumps and cooling towers are off, which makes no sense.
  • Chillers cool the chilled water even though the condenser loop is off.
  • Chiller Condenser Inlet Temperature is constant throughout the year (25.74°C for Chiller1 and 25.84°C for Chiller2), which is the weirdest thing in my model. Chillers cool chilled water without running cooling towers probably due to this constant condenser inlet temperature, but I don't know why the temperature at this node is constant.
  • Unmet hours are not detected even though the condenser loop is off.
  • Free convection in CoolingTower:TwoSpeed is not modelld.
  • Plant Loop Volume is autosized. I hardsized it to 0m3 as a trial, but the problem was not solved.

The charts below are one-week extracts of the simulation results in summer.

Cooling towers and condenser pumps are off.

image description

Chiller Condenser Inlet Temperature and Cooling Tower Outlet Temperature do not match at all.

image description

I have put the idf files here. Their version is V9-6-0. The model with continuous pumps is just for comparision.

I have modelled similar systems several times before, but this is the first time I have this problem. Any suggestion for solving this problem would be appreciated.

Chiller is ON but Cooling Tower is OFF

I got stuck over the weird behavior of my model. My model is a small office building with the following chilled water loop and condenser water loops.

image description

I bullet-point the situation.

  • The problem is that cooling towers and condenser pumps are off even when there is a cooling demand on the chilled water loop and the chiller is operating. The annual end use of Pumps and Heat Rejection is extremely small.
  • The problem occurred after I changed Pump Control Type from Continuous to Intermittent.
  • When there is a cooling demand on the chilled water loop, a cooling demand on the condenser water loop is 0.
  • There is a lot of Chiller Condenser Heat Transfer even though the condenser pumps and cooling towers are off, which makes no sense.
  • Chillers cool the chilled water even though the condenser loop is off.
  • Chiller Condenser Inlet Temperature is constant throughout the year (25.74°C for Chiller1 and 25.84°C for Chiller2), which is the weirdest thing in my model. Chillers cool chilled water without running cooling towers probably due to this constant condenser inlet temperature, but I don't know why the temperature at this node is constant.
  • Unmet hours are not detected even though the condenser loop is off.
  • Free convection in CoolingTower:TwoSpeed is not modelld.
  • Plant Loop Volume is autosized. I hardsized it to 0m3 as a trial, but the problem was not solved.

The charts below are one-week extracts of the simulation results in summer.

Cooling towers and condenser pumps are off.

image description

Chiller Condenser Inlet Temperature and Cooling Tower Outlet Temperature do not match at all.

image description

I have put the idf files here. Their version is V9-6-0. The model with continuous pumps is just for comparision.

I have modelled similar systems several times before, but this is the first time I have this problem. Any suggestion for solving this problem would be appreciated.

Chiller is ON but Cooling Tower is OFF

I got stuck over the weird behavior of my model. My model is a small office building with the following chilled water loop and condenser water loops.

image description

I bullet-point the situation.

  • The problem is that cooling towers and condenser pumps are off even when there is a cooling demand on the chilled water loop and the chiller is operating. The annual end use of Pumps and Heat Rejection is extremely small.
  • The problem occurred after I changed Pump Control Type from Continuous to Intermittent.
  • When there is a cooling demand on the chilled water loop, a cooling demand on the condenser water loop is 0.
  • There is a lot of Chiller Condenser Heat Transfer even though the condenser pumps and cooling towers are off, which makes no sense.
  • Chillers cool the chilled water even though the condenser loop is off.
  • Chiller Condenser Inlet Temperature is constant throughout the year (25.74°C for Chiller1 and 25.84°C for Chiller2), which is the weirdest thing in my model. Chillers cool chilled water without running cooling towers probably due to this constant condenser inlet temperature, but I don't know why the temperature at this node is constant.
  • Unmet hours are not detected even though the condenser loop is off.
  • Free convection in CoolingTower:TwoSpeed is not modelld.
  • Plant Loop Volume is autosized. I hardsized it to 0m3 as a trial, but the problem was not solved.

The charts below are one-week extracts of the simulation results in summer.

Cooling towers and condenser pumps are off.

image description

Chiller Condenser Inlet Temperature and Cooling Tower Outlet Temperature do not match at all.

image description

I have put the idf files here. Their version is V9-6-0. The model with continuous pumps is just for comparision. I closed the link.

I have modelled similar systems several times before, but this is the first time I have this problem. Any suggestion for solving this problem would be appreciated.