I got stuck over the weird behavior of my model. My model is a small office building with the following chilled water loop and condenser water loops.
I bullet-point the situation.
- The problem is that cooling towers and condenser pumps are off even when there is a cooling demand on the chilled water loop and the chiller is operating. The annual end use of Pumps and Heat Rejection is extremely small.
- The problem occurred after I changed Pump Control Type from
Continuous
toIntermittent
. - When there is a cooling demand on the chilled water loop, a cooling demand on the condenser water loop is 0.
- There is a lot of
Chiller Condenser Heat Transfer
even though the condenser pumps and cooling towers are off, which makes no sense. - Chillers cool the chilled water even though the condenser loop is off.
Chiller Condenser Inlet Temperature
is constant throughout the year (25.74°C for Chiller1 and 25.84°C for Chiller2), which is the weirdest thing in my model. Chillers cool chilled water without running cooling towers probably due to this constant condenser inlet temperature, but I don't know why the temperature at this node is constant.- Unmet hours are not detected even though the condenser loop is off.
Free convection
inCoolingTower:TwoSpeed
is not modelld.Plant Loop Volume
is autosized. I hardsized it to 0m3 as a trial, but the problem was not solved.
The charts below are one-week extracts of the simulation results in summer.
Cooling towers and condenser pumps are off.
Chiller Condenser Inlet Temperature
and Cooling Tower Outlet Temperature
do not match at all.
I have put the idf files here. Their version is V9-6-0. The model with continuous pumps is just for comparision.
I have modelled similar systems several times before, but this is the first time I have this problem. Any suggestion for solving this problem would be appreciated.