Coincident Sizing Factor Mode

My model has PlantLoop (chillers) and CondenserLoop (cooling towers). I did sizing runs in three different settings.

  1. NonCoincident plan sizing
  2. Coincident plant sizing, and Coincident Sizing Factor Mode is None
  3. Coincident plant sizing, and Coincident Sizing Factor Mode is GlobalCoolingSizingFactor

Sizing:Parameters Cooling Sizing Factor is 1.15.

The autosized chiller capacities are shown in the html files as follows.

image description

"NonCoincident" chiller capacity and "Coincident, None" chiller capacity are the same, but it is not addressed in this post. It's probebly because internal loads are more dominant than solar load, and the cooling demand in each zone peaks at the same time. All zones are following the same load schedule.

My question is about Coincident Sizing Factor Mode.

My assumption was that:

  • If I choose None, the autosized chiller capacity would be equal to the coincident peak demand.
  • If I choose NonCoincident, the autosized chiller capacity would be 1.15 times the coincident peak demand.

However, the simulation results suggest that:

  • When I chose None, The autosized chiller capacity = The coincident peak demand x 1.15
  • When I chose GlobalCoolingSizingFactor, The autosized chiller capacity = The coincident peak demand x 1.15 x 1.15

Are these the intended function of Coincident Sizing Factor Mode? If that's the case, I should choose None. Who would want to multiply the sizing factor twice?

Coincident Sizing Factor Mode

My model has PlantLoop (chillers) and CondenserLoop (cooling towers). I did sizing runs in three different settings.

  1. NonCoincident plan sizing
  2. Coincident plant sizing, and Coincident Sizing Factor Mode is None
  3. Coincident plant sizing, and Coincident Sizing Factor Mode is GlobalCoolingSizingFactor

Sizing:Parameters Cooling Sizing Factor is 1.15.

The autosized chiller capacities are shown in the html files as follows.

image descriptionimage description

"NonCoincident" chiller capacity and "Coincident, None" chiller capacity are the same, but it is not addressed in this post. It's probebly because internal loads are more dominant than solar load, and the cooling demand in each zone peaks at the same time. All zones are following the same load schedule.

My question is about Coincident Sizing Factor Mode.

My assumption was that:

  • If I choose None, the autosized chiller capacity would be equal to the coincident peak demand.
  • If I choose NonCoincident, the autosized chiller capacity would be 1.15 times the coincident peak demand.

However, the simulation results suggest that:

  • When I chose None, The autosized chiller capacity = The coincident peak demand x 1.15
  • When I chose GlobalCoolingSizingFactor, The autosized chiller capacity = The coincident peak demand x 1.15 x 1.15

Are these the intended function of Coincident Sizing Factor Mode? If that's the case, I should choose None. Who would want to multiply the sizing factor twice?

Coincident Sizing Factor Mode

My model has PlantLoop (chillers) and CondenserLoop (cooling towers). I did sizing runs in three different settings.

  1. NonCoincident plan sizing
  2. Coincident plant sizing, and Coincident Sizing Factor Mode is None
  3. Coincident plant sizing, and Coincident Sizing Factor Mode is GlobalCoolingSizingFactor

Sizing:Parameters Cooling Sizing Factor is 1.15.

The autosized chiller capacities are shown in the html files as follows.

image description

"NonCoincident" chiller capacity and "Coincident, None" chiller capacity are the same, but it is not addressed in this post. It's probebly because internal loads are more dominant is approximately 1% smaller than solar load, "NonCoincident" chiller capacity. I think Coincident plant sizing worked properly. Of course, I made Do HVAC Sizing Simulation for Sizing Periods Yes and the cooling demand in each zone peaks at the same time. All zones are following the same load schedule.Type of Zone Sum to Use of all AirLoops Coincident.

My question is about Coincident Sizing Factor Mode.

My assumption was that:

  • If I choose None, the autosized chiller capacity would be equal to the coincident peak demand.
  • If I choose NonCoincident, the autosized chiller capacity would be 1.15 times the coincident peak demand.

However, the simulation results suggest that:

  • When I chose None, The autosized chiller capacity = The coincident peak demand x 1.15
  • When I chose GlobalCoolingSizingFactor, The autosized chiller capacity = The coincident peak demand x 1.15 x 1.15

Are these the intended function of Coincident Sizing Factor Mode? If that's the case, I should choose None. Who would want to multiply the sizing factor twice?

Coincident Sizing Factor Mode

My model has PlantLoop (chillers) and CondenserLoop (cooling towers). I did sizing runs in three different settings.

  1. NonCoincident plan sizing
  2. Coincident plant sizing, and Coincident Sizing Factor Mode is None
  3. Coincident plant sizing, and Coincident Sizing Factor Mode is GlobalCoolingSizingFactor

Sizing:Parameters Cooling Sizing Factor is 1.15.

The autosized chiller capacities are shown in the html files as follows.

image descriptionimage description

"Coincident, None" chiller capacity is approximately 1% smaller than "NonCoincident" chiller capacity. I think Coincident plant sizing worked properly. Of course, I made Do HVAC Sizing Simulation for Sizing Periods Yes and Type of Zone Sum to Use of all AirLoops Coincident.

My question is about Coincident Sizing Factor Mode.

My assumption was that:

  • If I choose None, the autosized chiller capacity would be equal to the coincident peak demand.
  • If I choose NonCoincident, the autosized chiller capacity would be 1.15 times the coincident peak demand.

However, the simulation results suggest that:

  • When I chose None, The autosized chiller capacity = The coincident peak demand x 1.15
  • When I chose GlobalCoolingSizingFactor, The autosized chiller capacity = The coincident peak demand x 1.15 x 1.15

Are these the intended function of Coincident Sizing Factor Mode? If that's the case, I should choose None. Who would want to multiply the sizing factor twice?

Coincident Sizing Factor Mode

My model has PlantLoop (chillers) and CondenserLoop (cooling towers). I did sizing runs in three different settings.

  1. NonCoincident plan sizing
  2. Coincident plant sizing, and Coincident Sizing Factor Mode is None
  3. Coincident plant sizing, and Coincident Sizing Factor Mode is GlobalCoolingSizingFactor

Sizing:Parameters Cooling Sizing Factor is 1.15.

The autosized chiller capacities are shown in the html files as follows.

image description

"Coincident, None" chiller capacity is approximately 1% smaller than "NonCoincident" chiller capacity. I think Coincident plant sizing worked properly. Of course, I made Do HVAC Sizing Simulation for Sizing Periods Yes and Type of Zone Sum to Use of all AirLoops Coincident.

My question is about Coincident Sizing Factor Mode.

My assumption was that:

  • If I choose None, the autosized chiller capacity would be equal to the coincident peak demand.
  • If I choose NonCoincident, the autosized chiller capacity would be 1.15 times the coincident peak demand.

However, the simulation results suggest that:

  • When I chose None, The autosized chiller capacity = The coincident peak demand x 1.15
  • When I chose GlobalCoolingSizingFactor, The autosized chiller capacity = The coincident peak demand x 1.15 x 1.15

Are these the intended function of Coincident Sizing Factor Mode? If that's the case, I should choose None. Who would want to multiply the sizing factor twice?