I have a sizing disagreement in my idf file, but I'm having trouble finding where I inputted the conflicting fields. Any ideas on where I should look? And here is a google drive link to the files.
Here is the relevant part of the ERR file:
************* SizeWaterCoil: Potential issue with equipment sizing for Coil:Cooling:Water LGSTORE1 ZN COOLING COIL
** ~~~ ** User-Specified Design Air Flow Rate [m3/s] = 0.79234
** ~~~ ** differs from Design Size Design Air Flow Rate [m3/s] = 0.87231
** ~~~ ** This may, or may not, indicate mismatched component sizes.
** ~~~ ** Verify that the value entered is intended and is consistent with other components.
Here is the relevant part of the EIO file:
Component Sizing Information, Coil:Cooling:Water, LGSTORE1 ZN COOLING COIL, Design Size Design Air Flow Rate [m3/s], 0.87231
Component Sizing Information, Coil:Cooling:Water, LGSTORE1 ZN COOLING COIL, User-Specified Design Air Flow Rate [m3/s], 0.79234
But the strange thing is I think those fields are autosized.
Not sure if these are important, but those conflicting flow rates appear elsewhere in the EIO file.
Zone Sizing Information, LGSTORE1 ZN, Heating, 16855.60896, 20226.73075, 0.72693, 0.87231, CLIMATE ZONE 12 ANN HTG 99.6% CONDNS DB, 12/21 13:00:00, -0.40000, 3.65329E-003, 348.38640, 30.00000, 0.41148, 0.00000
Component Sizing Information, ZoneHVAC:FourPipeFanCoil, LGSTORE1 ZN FAN COIL, Design Size Maximum Supply Air Flow Rate [m3/s], 0.87231
Component Sizing Information, Fan:OnOff, LGSTORE1 ZN SUPPLY FAN, Design Size Maximum Flow Rate [m3/s], 0.87231
Zone Sizing Information, LGSTORE1 ZN, Cooling, 8994.03839, 10792.84607, 0.66028, 0.79234, CLIMATE ZONE 12 ANN CLG .4% CONDNS DB=>MWB, 7/21 15:00:00, 37.90000, 9.07726E-003, 348.38640, 30.00000, 0.41148, 0.00000
However, I think those fields are also autosized.