Any guidance on how can I use an EMS program to override behaviour of a setpoint manager in heating mode, to increase airflow rate through each VAV up to maximum available would be helpful.
My goal is to create an EMS program that increases VAV airflow rates up to their maximum available so that there is more hot air during morning warmup. The problem I am having is that the zones are taking ~3 hours to warm up because they are not getting enough hot air. The reheat coils are working, delivering hot air, but the flow rates are stuck on min.
I am using a SetpointManager:WarmestTemperatureFlow
- Temperature first
- Minimum TurndownRatio 0.35
From the docs, In heating mode, this SPM will set minimum flow:
"...For TemperatureFirst the manager tries to find the highest setpoint temperature that will satisfy all the zone cooling loads at minimum supply air flow rate. If this setpoint temperature is less than the minimum, the setpoint temperature is set to the minimum, and the supply air flow rate is increased to meet the loads... ""
The .edd tells me that there is no Actuator for 'Minimum Airflow Ratio'. Best I can do is Mass Flow Rate or Minimum Available Mass Flow Rate. My tests so far show that these actuators have no effect.
Can someone familiar with the inner working of the HVAC code comment on how the code takes the value for the 'Minimum Turndown Ratio' set in the SPM and from it sets the VAV flow rates? Links to the source code that does this would be helpful.
Screenshot of the AirLoop
EnergyPlus IDF (zipped idf mascerading as a png). C:\fakepath\inzip.png