HVACTemplate:VAV doesn't introduce Outdoor Air

I am modelling the VAV with water cooled chiller.
I specify the Outdoor air flow rate in DesignSpecification:OutdoorAir as below

DesignSpecification:OutdoorAir,
Office_OA,               !- Name
Sum,                     !- Outdoor Air Method
0.00325,                 !- Outdoor Air Flow per Person {m3/s-person}
0.00039;                 !- Outdoor Air Flow per Zone Floor Area {m3/s-m2}

and refer this specification in HVACTemplate:Zone:VAV as below

HVACTemplate:Zone:VAV,
A_LZ_OfficeN,            !- Zone Name
A_LZ_Sys,                !- Template VAV System Name
Off_SP,                  !- Template Thermostat Name
autosize,                !- Supply Air Maximum Flow Rate {m3/s}
,                        !- Zone Heating Sizing Factor
,                        !- Zone Cooling Sizing Factor
Constant,                !- Zone Minimum Air Flow Input Method
0.4,                     !- Constant Minimum Air Flow Fraction
,                        !- Fixed Minimum Air Flow Rate {m3/s}
,                        !- Minimum Air Flow Fraction Schedule Name
DetailedSpecification,   !- Outdoor Air Method
0.00944,                 !- Outdoor Air Flow Rate per Person {m3/s}
,                        !- Outdoor Air Flow Rate per Zone Floor Area {m3/s-m2}
,                        !- Outdoor Air Flow Rate per Zone {m3/s}
None,                    !- Reheat Coil Type
,                        !- Reheat Coil Availability Schedule Name
Reverse,                 !- Damper Heating Action
,                        !- Maximum Flow per Zone Floor Area During Reheat {m3/s-m2}
,                        !- Maximum Flow Fraction During Reheat
,                        !- Maximum Reheat Air Temperature {C}
Office_OA,               !- Design Specification Outdoor Air Object Name for Control
,                        !- Supply Plenum Name
,                        !- Return Plenum Name
None,                    !- Baseboard Heating Type
,                        !- Baseboard Heating Availability Schedule Name
autosize,                !- Baseboard Heating Capacity {W}
SystemSupplyAirTemperature,  !- Zone Cooling Design Supply Air Temperature Input Method
12.8,                    !- Zone Cooling Design Supply Air Temperature {C}
11.11,                   !- Zone Cooling Design Supply Air Temperature Difference {deltaC}
SupplyAirTemperature,    !- Zone Heating Design Supply Air Temperature Input Method
50,                      !- Zone Heating Design Supply Air Temperature {C}
30;                      !- Zone Heating Design Supply Air Temperature Difference {deltaC}

However, checking the result Standard 62.1 Summarybelow, it seems that no Outdoor Air is introduced
image description

Can anyone tell me why and how I can fix this problem?