Energy Plus modelling HVAC without dehumidification

Hi all! I'm trying to model a very simple air conditioning device in EnergyPlus, I don't have anything specific about the system yet, apart the fact that it is just a cooling device. I use: HVACTemplate:Zone:IdealLoadsAirSystem the cooling works just fine but when I look at the relative humidity it looks like the humidity stays constantly at 45%. The climate is very hot and humid, therefore if the air is just cooled the relative humidity should rise, right? I put the Dehumidification Control Type to 'None' So I am wondering why the relative humidity is so low. Perhaps I overlooked something. Can anybody help me with this? Thanks for your help!!!

Here are my settings:

HVACTemplate:Zone:IdealLoadsAirSystem, Thermal Zone 1 !- Zone Name thermostat, !- Template Thermostat Name Assembly HVAC, !- System Availability Schedule Name 50, !- Maximum Heating Supply Air Temperature {C} 13, !- Minimum Cooling Supply Air Temperature {C} 0.02, !- Maximum Heating Supply Air Humidity Ratio {kgWater/kgDryAir} 0.0077, !- Minimum Cooling Supply Air Humidity Ratio {kgWater/kgDryAir} NoLimit, !- Heating Limit 0, !- Maximum Heating Air Flow Rate {m3/s} 0, !- Maximum Sensible Heating Capacity {W} NoLimit, !- Cooling Limit , !- Maximum Cooling Air Flow Rate {m3/s} 0, !- Maximum Total Cooling Capacity {W} Assembly HVAC, !- Heating Availability Schedule Name Assembly HVAC, !- Cooling Availability Schedule Name None, !- Dehumidification Control Type 0.7, !- Cooling Sensible Heat Ratio {dimensionless} 60, !- Dehumidification Setpoint {percent} None, !- Humidification Control Type 30, !- Humidification Setpoint {percent} None, !- Outdoor Air Method 0.00944, !- Outdoor Air Flow Rate per Person {m3/s} , !- Outdoor Air Flow Rate per Zone Floor Area {m3/s-m2} , !- Outdoor Air Flow Rate per Zone {m3/s} , !- Design Specification Outdoor Air Object Name None, !- Demand Controlled Ventilation Type NoEconomizer, !- Outdoor Air Economizer Type None, !- Heat Recovery Type 0.7, !- Sensible Heat Recovery Effectiveness {dimensionless} 0.65; !- Latent Heat Recovery Effectiveness {dimensionless} image descriptionimage description

Energy Plus modelling HVAC without dehumidification

Hi all! I'm trying to model a very simple air conditioning device in EnergyPlus, I don't have anything specific about the system yet, apart the fact that it is just a cooling device. I use: HVACTemplate:Zone:IdealLoadsAirSystem the cooling works just fine but when I look at the relative humidity it looks like the humidity stays constantly at 45%. The climate is very hot and humid, therefore if the air is just cooled the relative humidity should rise, right? I put the Dehumidification Control Type to 'None' So I am wondering why the relative humidity is so low. Perhaps I overlooked something. Can anybody help me with this? Thanks for your help!!!

Here are my settings:

HVACTemplate:Zone:IdealLoadsAirSystem, Thermal Zone 1 !- Zone Name thermostat, !- Template Thermostat Name Assembly HVAC, !- System Availability Schedule Name 50, !- Maximum Heating Supply Air Temperature {C} 13, !- Minimum Cooling Supply Air Temperature {C} 0.02, !- Maximum Heating Supply Air Humidity Ratio {kgWater/kgDryAir} 0.0077, !- Minimum Cooling Supply Air Humidity Ratio {kgWater/kgDryAir} NoLimit, !- Heating Limit 0, !- Maximum Heating Air Flow Rate {m3/s} 0, !- Maximum Sensible Heating Capacity {W} NoLimit, !- Cooling Limit , !- Maximum Cooling Air Flow Rate {m3/s} 0, !- Maximum Total Cooling Capacity {W} Assembly HVAC, !- Heating Availability Schedule Name Assembly HVAC, !- Cooling Availability Schedule Name None, !- Dehumidification Control Type 0.7, !- Cooling Sensible Heat Ratio {dimensionless} 60, !- Dehumidification Setpoint {percent} None, !- Humidification Control Type 30, !- Humidification Setpoint {percent} None, !- Outdoor Air Method 0.00944, !- Outdoor Air Flow Rate per Person {m3/s} , !- Outdoor Air Flow Rate per Zone Floor Area {m3/s-m2} , !- Outdoor Air Flow Rate per Zone {m3/s} , !- Design Specification Outdoor Air Object Name None, !- Demand Controlled Ventilation Type NoEconomizer, !- Outdoor Air Economizer Type None, !- Heat Recovery Type 0.7, !- Sensible Heat Recovery Effectiveness {dimensionless} 0.65; !- Latent Heat Recovery Effectiveness {dimensionless} image descriptionimage descriptionrelative humidity temperature

Energy Plus modelling HVAC without dehumidification

Hi all! I'm trying to model a very simple air conditioning device in EnergyPlus, I don't have anything specific about the system yet, apart the fact that it is just a cooling device. I use: HVACTemplate:Zone:IdealLoadsAirSystem the cooling works just fine but when I look at the relative humidity it looks like the humidity stays constantly at 45%. The climate is very hot and humid, therefore if the air is just cooled the relative humidity should rise, right? I put the Dehumidification Control Type to 'None' So I am wondering why the relative humidity is so low. Perhaps I overlooked something. Can anybody help me with this? Thanks for your help!!!

Here are my settings:

HVACTemplate:Zone:IdealLoadsAirSystem,
   Thermal Zone 1   !- Zone Name
   thermostat,              !- Template Thermostat Name
   Assembly HVAC,           !- System Availability Schedule Name
   50,                      !- Maximum Heating Supply Air Temperature {C}
   13,                      !- Minimum Cooling Supply Air Temperature {C}
   0.02,                    !- Maximum Heating Supply Air Humidity Ratio {kgWater/kgDryAir}
   0.0077,                  !- Minimum Cooling Supply Air Humidity Ratio {kgWater/kgDryAir}
   NoLimit,                 !- Heating Limit
   0,                       !- Maximum Heating Air Flow Rate {m3/s}
   0,                       !- Maximum Sensible Heating Capacity {W}
   NoLimit,                 !- Cooling Limit
   ,                        !- Maximum Cooling Air Flow Rate {m3/s}
   0,                       !- Maximum Total Cooling Capacity {W}
   Assembly HVAC,           !- Heating Availability Schedule Name
   Assembly HVAC,           !- Cooling Availability Schedule Name
   None,                    !- Dehumidification Control Type
   0.7,                     !- Cooling Sensible Heat Ratio {dimensionless}
   60,                      !- Dehumidification Setpoint {percent}
   None,                    !- Humidification Control Type
   30,                      !- Humidification Setpoint {percent}
   None,                    !- Outdoor Air Method
   0.00944,                 !- Outdoor Air Flow Rate per Person {m3/s}
   ,                        !- Outdoor Air Flow Rate per Zone Floor Area {m3/s-m2}
   ,                        !- Outdoor Air Flow Rate per Zone {m3/s}
   ,                        !- Design Specification Outdoor Air Object Name
   None,                    !- Demand Controlled Ventilation Type
   NoEconomizer,            !- Outdoor Air Economizer Type
   None,                    !- Heat Recovery Type
   0.7,                     !- Sensible Heat Recovery Effectiveness {dimensionless}
   0.65;                    !- Latent Heat Recovery Effectiveness {dimensionless}

relative humidity temperature

Energy Plus modelling HVAC without dehumidification

Hi all! I'm trying to model a very simple air conditioning device in EnergyPlus, I don't have anything specific about the system yet, apart the fact that it is just a cooling device. I use: HVACTemplate:Zone:IdealLoadsAirSystem HVACTemplate:Zone:IdealLoadsAirSystem the cooling works just fine but when I look at the relative humidity it looks like the humidity stays constantly at 45%.

The climate is very hot and humid, therefore if the air is just cooled the relative humidity should rise, right? I put the Dehumidification Control Type Type to 'None' So None so I am wondering why the relative humidity is so low. Perhaps I overlooked something. Can anybody help me with this? Thanks for your help!!!this?

Here are my settings:

HVACTemplate:Zone:IdealLoadsAirSystem,
  Thermal Zone 1   !- Zone Name
  thermostat,              !- Template Thermostat Name
  Assembly HVAC,           !- System Availability Schedule Name
  50,                      !- Maximum Heating Supply Air Temperature {C}
  13,                      !- Minimum Cooling Supply Air Temperature {C}
  0.02,                    !- Maximum Heating Supply Air Humidity Ratio {kgWater/kgDryAir}
  0.0077,                  !- Minimum Cooling Supply Air Humidity Ratio {kgWater/kgDryAir}
  NoLimit,                 !- Heating Limit
  0,                       !- Maximum Heating Air Flow Rate {m3/s}
  0,                       !- Maximum Sensible Heating Capacity {W}
  NoLimit,                 !- Cooling Limit
  ,                        !- Maximum Cooling Air Flow Rate {m3/s}
  0,                       !- Maximum Total Cooling Capacity {W}
  Assembly HVAC,           !- Heating Availability Schedule Name
  Assembly HVAC,           !- Cooling Availability Schedule Name
  None,                    !- Dehumidification Control Type
  0.7,                     !- Cooling Sensible Heat Ratio {dimensionless}
  60,                      !- Dehumidification Setpoint {percent}
  None,                    !- Humidification Control Type
  30,                      !- Humidification Setpoint {percent}
  None,                    !- Outdoor Air Method
  0.00944,                 !- Outdoor Air Flow Rate per Person {m3/s}
  ,                        !- Outdoor Air Flow Rate per Zone Floor Area {m3/s-m2}
  ,                        !- Outdoor Air Flow Rate per Zone {m3/s}
  ,                        !- Design Specification Outdoor Air Object Name
  None,                    !- Demand Controlled Ventilation Type
  NoEconomizer,            !- Outdoor Air Economizer Type
  None,                    !- Heat Recovery Type
  0.7,                     !- Sensible Heat Recovery Effectiveness {dimensionless}
  0.65;                    !- Latent Heat Recovery Effectiveness {dimensionless}

relative humidity temperature