How to Model Supply Air Temperature Reset?
Could someone please confirm if I am modeling my supply air temperature reset correctly for a LEED baseline model in OpenStudio 1.11? It should follow ASHRAE 90.1-2007 Section G3.1.3.12 which states, "The air temperature for cooling shall be reset higher by 5°F under the minimum cooling load conditions." My zone cooling setpoint is 75°F and the design cooling supply air temperature is 55°F. I am using SetpointManager:Warmest with the minimum setpoint temperature at 55°F and the maximum setpoint temperature at 60°F. image description
I am following other threads and documentation such as
https://unmethours.com/question/14152/setpoint-manager-openstudio/ http://bigladdersoftware.com/epx/docs/8-4/input-output-reference/group-setpoint-managers.html#setpointmanagerwarmest