How to Model Supply Air Temperature Reset?

asked 2016-05-31 16:43:42 -0500

updated 2016-05-31 19:55:52 -0500

Could someone please confirm if I am modeling my supply air temperature reset correctly for a LEED baseline model in OpenStudio 1.11? It should follow ASHRAE 90.1-2007 Section G3.1.3.12 which states, "The air temperature for cooling shall be reset higher by 5°F under the minimum cooling load conditions." My zone cooling setpoint is 75°F and the design cooling supply air temperature is 55°F. I am using SetpointManager:Warmest with the minimum setpoint temperature at 55°F and the maximum setpoint temperature at 60°F. image description

I am following other threads and documentation such as

https://unmethours.com/question/14152... http://bigladdersoftware.com/epx/docs...

edit retag flag offensive close merge delete

Comments

2

Plot the supply air temperature versus air loop flow rate and specific zone air flow rate to see how the HVAC system responds.

rraustad gravatar image rraustad  ( 2016-05-31 19:41:05 -0500 )edit

1 Answer

Sort by » oldest newest most voted
2

answered 2016-05-31 19:54:57 -0500

Correct, the SetpointManager:Warmest satisfies the PRM requirement. It's also how the OpenStudio Standards create the baseline systems 5-8.

edit flag offensive delete link more

Comments

@MatthewSteen What if I have two different setpoint for two thermal zones, connected to a single AHU?

Gio gravatar image Gio  ( 2017-08-01 04:09:05 -0500 )edit