Heat Pumps with Variable Speed Fan

Hello,

OS does not have an option of variable speed fan control for water to air heat pumps. Therefore, I tried modeling the variable speed control in E+ text based editor, but got the following error.

" * Severe * MixedAir: Missing temperature setpoint for economizer controller OAC BAG DUMP * Severe * Node Referenced (by Controller)=NODE 189 * ~~~ * use a Setpoint Manager with Control Variable = "Temperature" to establish a setpoint at the mixed air node."

This error showed up after I specified the follwing schedule for "Supply Air Fan Operating Mode Schedule Name", which is needed for "Fan:VariableVolume". Production Schedule, !- Supply Air Fan Operating Mode Schedule Name

I don't understand what E+ is looking for. How could a setpoint be specified for mixed air? Also, why didn't this error show up when a setpoint controller was not specified in OS? Looks like this is an advanced level of HVAC requirement by E+ after variable speed control and fan operating schedule is specified.

Any feedback on this will be helpful!

Regards, Pranav

Heat Pumps with Variable Speed Fan

Hello,

OS does not have an option of variable speed fan control for water to air heat pumps. Therefore, I tried modeling the variable speed control in E+ text based editor, but got the following error.

" * Severe * MixedAir: Missing temperature setpoint for economizer controller OAC BAG DUMP * Severe * Node Referenced (by Controller)=NODE 189 * ~~~ * use a Setpoint Manager with Control Variable = "Temperature" to establish a setpoint at the mixed air node."

This error showed up after I specified the follwing schedule for "Supply Air Fan Operating Mode Schedule Name", which is needed for "Fan:VariableVolume". Production Schedule, !- Supply Air Fan Operating Mode Schedule Name

I don't understand what E+ is looking for. How could a setpoint be specified for mixed air? Also, why didn't this error show up when a setpoint controller was not specified in OS? Looks like this is an advanced level of HVAC requirement by E+ after variable speed control and fan operating schedule is specified.

Any feedback on this will be helpful!

Regards, Pranav

Heat Pumps with Variable Speed Fan

Hello,

OS does not have an option of variable speed fan control for water to air heat pumps. Therefore, I tried modeling the variable speed control in E+ text based editor, but got the following error.

"

* Severe * MixedAir: Missing temperature setpoint for economizer controller OAC BAG DUMP * Severe * Node Referenced (by Controller)=NODE 189 * ~~~ * use a Setpoint Manager with Control Variable = "Temperature" to establish a setpoint at the mixed air node."

This error showed up after I specified the follwing schedule for "Supply Air Fan Operating Mode Schedule Name", which is needed for "Fan:VariableVolume". Production Schedule, !- Supply Air Fan Operating Mode Schedule Name

I don't understand what E+ is looking for. How could a setpoint be specified for mixed air? Also, why didn't this error show up when a setpoint controller was not specified in OS? Looks like this is an advanced level of HVAC requirement by E+ after variable speed control and fan operating schedule is specified.

Any feedback on this will be helpful!

Regards, Pranav

Heat Pumps with Variable Speed Fan

Hello,

OS does not have an option of variable speed fan control for water to air heat pumps. Therefore, I tried modeling the variable speed control in E+ text based editor, but got the following error.

* Severe * MixedAir: Missing temperature setpoint for economizer controller OAC BAG DUMP * Severe * Node Referenced (by Controller)=NODE 189 * ~~~ * use a Setpoint Manager with Control Variable = "Temperature" to establish a setpoint at the mixed air node."

This error showed up after I specified the follwing schedule for "Supply Air Fan Operating Mode Schedule Name", which is needed for "Fan:VariableVolume". Production Schedule, !- Supply Air Fan Operating Mode Schedule Name

I don't understand what E+ is looking for. How could a setpoint be specified for mixed air? Also, why didn't this error show up when a setpoint controller was not specified in OS? Looks like this is an advanced level of HVAC requirement by E+ after variable speed control and fan operating schedule is specified.

Any feedback on this will be helpful!

Regards, Pranav

Heat Pumps with Variable Speed Fan

Hello,

OS does not have an option of variable speed fan control for water to air heat pumps. Therefore, I tried modeling the variable speed control in E+ text based editor, but got the following error.

* Severe * MixedAir: Missing temperature setpoint for economizer controller OAC BAG DUMP * Severe * Node Referenced (by Controller)=NODE 189 * ~~~ * use a Setpoint Manager with Control Variable = "Temperature" to establish a setpoint at the mixed air node."

This error showed up after I specified the follwing schedule for "Supply Air Fan Operating Mode Schedule Name", which is needed for "Fan:VariableVolume". Production Schedule, !- Supply Air Fan Operating Mode Schedule Name

I don't understand what E+ is looking for. How could a setpoint be specified for mixed air? Also, why didn't this error show up when a setpoint controller was not specified in OS? Looks like this is an advanced level of HVAC requirement by E+ after variable speed control and fan operating schedule is specified.

Any feedback on this will be helpful!

Regards, Pranav