Turn off outside air for air loop during unoccupied period

In case of an office building, my system should be running 6am to 10pm, and should cycle with the load at night, except I want to make sure I don't have any outside air during the night cycle (unless economizer is activated for cooling).

Let's call my schedule HVAC Operation Schedule, and it has a value of 1 between 6 am and 10pm, and 0 otherwise

I've set an AvailabilityManager:NightCycle for the airloop an assigned HVAC Operation Schedule as fan schedule.

I figured that to turn off the outside air I should assign the HVAC Operation Schedule to the Controller:OutdoorAir.

Instinctively, I have set this schedule to the Maximum Fraction of Outdoor Air Schedule Name field. This made sense to me: if I say the maximum is zero, it should be turned off!

This doesn't seem to be doing what I want, since when cycling at nighttime, it's apparently still pulling Outside Air.

After investigation in the documentation and confirming it by looking at the DOE Commercial reference buildings, it seems that the field I should use is Minimum Outdoor Air Schedule Name. From the docs:

Minimum Outdoor Air Schedule Name

The name of a schedule which uses decimal values (0.0 1.0). These values are multiplied by the minimum outdoor air flow rate. This schedule is useful for reducing the outdoor air flow rate to zero during unoccupied or start up hours. If this field is not entered, the minimum outdoor air flow rate either remains constant during the simulation period (Minimum Outdoor Air Control Type = FixedMinimum) or varies in proportion to the supply air flow rate (Minimum Outdoor Air Control Type = ProportionalMinimum).

I'm having trouble following the logic here... Can someone enlighten me?

Turn off outside air for air loop during unoccupied period

In case of an office building, my system should be running 6am to 10pm, and should cycle with the load at night, except I want to make sure I don't have any outside air during the night cycle (unless economizer is activated for cooling).

Let's call my schedule HVAC Operation Schedule, and it has a value of 1 between 6 am and 10pm, and 0 otherwise

I've set an AvailabilityManager:NightCycle for the airloop an assigned HVAC Operation Schedule as fan schedule.

I figured that to turn off the outside air I should assign the HVAC Operation Schedule to the Controller:OutdoorAir.

Instinctively, I have set this schedule to the Maximum Fraction of Outdoor Air Schedule Name field. This made sense to me: if I say the maximum is zero, it should be turned off!

This doesn't seem to be doing what I want, since when cycling at nighttime, it's apparently still pulling Outside Air.

After investigation in the documentation and confirming it by looking at the DOE Commercial reference buildings, it seems that the field I should use is Minimum Outdoor Air Schedule Name. From the docs:

Minimum Outdoor Air Schedule Name

The name of a schedule which uses decimal values (0.0 1.0). These values are multiplied by the minimum outdoor air flow rate. This schedule is useful for reducing the outdoor air flow rate to zero during unoccupied or start up hours. If this field is not entered, the minimum outdoor air flow rate either remains constant during the simulation period (Minimum Outdoor Air Control Type = FixedMinimum) or varies in proportion to the supply air flow rate (Minimum Outdoor Air Control Type = ProportionalMinimum).

I'm having trouble following the logic here... Can someone enlighten me?