OA below specified minimum for zone served by VAV

I'm attempting to model a pretty simple multiple zone VAV system in eQuest. This system serves a large gymnasium and a few small offices and storage rooms in a cold climate (Calgary, Canada). The problem I'm having is that the outdoor air rate being supplied to the gymnasium is below the minimum I've specified.

I've selected the "Pkgd Var Vol" system type, and specified minimum outdoor air flow rates for each zone (6313 cfm in the case of the gym). At the system level, I've selected the "fraction of design flow" OA control method, and the "set by critical zone" OA sizing method. The gymnasium zone terminal has a reheat coil, and the zone also has baseboard heaters.

I've set the minimum supply air flow for the gymnasium zone to 0.4 cfm/ft2, which works out to 2652 cfm. The problem is that this number seems to be taking precedence over the required O/A of 6313 when DOE-2 determines the zone's minimum flow. (Because there are baseboards in the zone, the S/A continually rides the minimum).

It seems to me that the "minimum" ought to be the larger of the specified minimum S/A and the minimum O/A... is this just not how it works? If so, is there any way to force eQuest/DOE-2 to work like this?