How to calculate thermal (cooling and heating) loads in EnergyPlus without designing HVAC system?

asked 2024-08-25 15:12:31 -0500

MHW's avatar

updated 2024-08-29 01:12:05 -0500

Hi,

I want to determine the overall cooling and heating load in my EnergyPlus model, without designing the actual HVAC system - this will serve as my baseline model, the results of which I can compare with "advanced" (modified) EnergyPlus model.

The only way I came across to do this is via defining an object in EnergyPlus called ZoneHVAC:IdealLoadsAirSystem.

Further, the Output:Variables which can help to estimate this are:

  1. Zone Ideal Loads Zone Total Heating Rate
  2. Zone Ideal Loads Zone Total Cooling Rate
  3. Zone Air System Sensible Heating Rate
  4. Zone Air System Sensible Cooling Rate

Can anyone from the community help me in understanding if I am on the right track pertaining to the above mentioned, if not, how can I achieve this effectively? - any sort of guidance will be welcomed and appreciated.

Apologies, if the question is not clear enough.

Thank you!

Edit-1:

image description

edit retag flag offensive close merge delete

Comments

@Denis Bourgeois thank you again, for clarifying my doubt on this. Regarding the files, I indeed referred to the "/5Zone_IdealLoadsAirSystems_ReturnPlenum.idf" - the same which you have referred to in your comment. It certainly was of help.

Another question, shouldn't both the sensible and latent thermal (cooling/heating) rates be taken into account for assessing the loads?

MHW's avatar MHW  ( 2024-08-27 12:53:12 -0500 )edit
1

"[...] shouldn't both the sensible and latent thermal (cooling/heating) rates be taken into account"? From the IO Reference: "All of the ZoneHVAC:IdealLoadsAirSystem loads and energy use are reported for Sensible Heating, Latent Heating, Total Heating, Sensible Cooling, Latent Cooling, and Total Cooling". I may be misunderstanding your question.

Denis Bourgeois's avatar Denis Bourgeois  ( 2024-08-27 15:51:05 -0500 )edit

@Denis Bourgeois actually what made me to ask this question is I was looking at the results generated by the EnergyPlus model for a weather environment classified as 1A. This is highly hot climate. When I compared the sensible and latent cooling loads, sensible loads turned out to be much higher - I was expecting latent cooling loads to be higher, but I understand this is mainly driven by the outdoor humidity than the People occupying the buildings? - I hope my question is clearer?

MHW's avatar MHW  ( 2024-08-28 01:15:14 -0500 )edit
1

@MHW, I would indeed expect outdoor humidity driving latent cooling loads (more so than internal loads) in CZ1A (hot & humid). Although this would ultimately depend on what's going on in that facility (e.g. greenhouse? industrial laundry/cleaning?), and on selected "Dehumidification Control" options. Fortunately, the ZoneHVAC:IdealLoadsAirSystem object allows you to output/compare "Outdoor Air" vs "Supply Air" vs "Zone" Latent Cooling Energy. You can do the same for Sensible or Total, allowing you to pinpoint when/where sensible vs latent loads are being picked up.

Denis Bourgeois's avatar Denis Bourgeois  ( 2024-08-28 05:41:23 -0500 )edit

@Denis Bourgeois perfect that clarified my doubts to a greater level. I think the "Humidification/Dehumidification Control" might be a factor too which influences the latent heating and cooling loads, as the aim is to maintain humidity close to 50%.

I have attached the image of the "IdealLoadsAirSystem" under Edit-1 of the original question. This is from my current (baseline) model. Since, the "Humidification Control" is chosen to be "None" - it might be leading to low latent thermal loads, correct me if I am wrong.

MHW's avatar MHW  ( 2024-08-28 10:31:59 -0500 )edit

1 Answer

Sort by ยป oldest newest most voted
1

answered 2024-09-02 14:49:13 -0500

updated 2024-09-02 15:01:15 -0500

MHW, I concatenated my initial August 26 comments as an answer to your original question. Cheers.


@MHW, you're correct on the use of ZoneHVAC:IdealLoadsAirSystem to address your needs. Note: I updated your Engineering Reference link to 24.1 (updated since from 8.0). I suggest you check out as well the 24.1 IO Reference:

  • how required energy is metered/reported
  • required fields
  • actual outputs
  • better documented in general

You may also find it insightful to consult related issues, past or current. And consulting any example file(s) that come with EnergyPlus is always useful.

(see above for follow-up Q/A)