Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
2

Simulating hybrid HVAC Systems

asked 2024-06-14 09:40:21 -0500

Mcheunn's avatar

I'm looking to simulate a home that runs on a hybrid HVAC system that uses an undersized GSHP to satisfy a base load and then the rest of the peak demands are met by an ASHP, boiler, or cooling tower - is there a way to easily implement this in BEopt/OpenStudio?

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
1

answered 2024-06-21 13:30:47 -0500

Greg Estep's avatar

I'm a designbuilder user, not BEopt or OpenStudio. This is how I would set it up:

Create a mixed water loop by using a plant loop with the load distribution scheme set to 1-sequential, and the plant loop demand calculation scheme set to 2-DualSetPointDeadband. Set the main plant loop setpoint manager to type 17-dual setpoint. I use high setpoint = 24C and low setpoint = 7C.

Then connect your components in series with appropriate setpoint managers. Connect the ground heat exchanger (GHE) first and use the same setpoint manager as the main plant loop. Then connect the boiler, and cooling tower, all with the same dual setpoint manager.

Set the plant equipment operation such that the GHE operation type is uncontrolled, the boiler is heating load, and cooling tower is cooling load.

In theory, as the load increases past the capacity of the GHE, the boiler or cooling tower will pick up the load.

I hope this helps. Greg

edit flag offensive delete link more

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Careers

Question Tools

1 follower

Stats

Asked: 2024-06-14 09:40:21 -0500

Seen: 88 times

Last updated: Jun 21