Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
2

Defining an Always-Open Entrance Exposed to Outdoor Conditions

asked 2024-04-26 08:19:31 -0500

Zakaria's avatar

updated 2024-04-30 09:44:53 -0500

Hellow everyone,

I am currently working on a construction model (here) that includes an always-open entrance that is directly exposed to outdoor conditions. I am seeking guidance on the appropriate method to define this opening to specify the properties of air flow through it.

Thank you in advance for any assistance you can provide.

image description

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
2

answered 2024-04-29 10:43:07 -0500

updated 2024-04-30 08:23:13 -0500

I would treat it as outdoors and include the surfaces on the sides, back, and top of the entrance as part of the envelope that separates the interior from the exterior of the building.

The top view layout of the building from ground level to the top of the entrance would be:

image description

edit flag offensive delete link more

Comments

Thanks @JasonGlazer for your response Could you possibly provide a more in-depth explanation? My knowledge of EnergyPlus is limited.

Here's what I've tried so far: I set up a very thin door construction for the entrance using the Material:NoMass object, with a thermal resistance of 0.00385 m2.K/W. However, it seems like this setup isn't quite realistic since it doesn't account for infiltration, given that the entrance is exposed to outdoor conditions.

Zakaria's avatar Zakaria  ( 2024-04-30 07:56:20 -0500 )edit

Forget the idea that the "entrance" is an interior room of the building and instead define the building perimeter to go inwards at that point.

JasonGlazer's avatar JasonGlazer  ( 2024-04-30 08:20:10 -0500 )edit

Thanks for the response! Just to clarify, I might not have explained the issue clearly.

I am modeling a refrigerated warehouse that is composed of 13 zones, 12 walk-in coolers, and a loading zone. The loading zone has an entrance that is always open (see figure above).

Sorry for any confusion.

Zakaria's avatar Zakaria  ( 2024-04-30 09:48:09 -0500 )edit

I am currently doing some refrigerated warehouse modeling. Have you tried looking at the RefrigeratedWarehouse example model in E+? Below are comments from the IDF.

! Refrigeration load is highly dependent upon infiltration rates (ACH). Air chillers ! and refrigeration systems oversized to allow possible increase above rates used here. ! An effective Air Barrier System has been assumed in selecting the rates modeled here. ! A common InfiltrationSchedule has been used for all zones with adjustments for ! likely use made using the ZoneInfiltration:DesignFlowRate objects.

sashadf1's avatar sashadf1  ( 2024-05-01 14:49:09 -0500 )edit

How about the AirFlowNetwork (AFN) model?

According to the EnergyPlus documentation, AFN is an advanced model designed to compute natural infiltration influenced by wind and forced air.

Can AFN be utilized to simulate infiltration through entrances?

I've looked into some EnergyPlus examples, but navigating them is challenging given my limited understanding of EnergyPlus. It's frustrating that explanatory documentation for the examples isn't available.

Zakaria's avatar Zakaria  ( 2024-05-03 04:21:53 -0500 )edit

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Training Workshops

Careers

Question Tools

1 follower

Stats

Asked: 2024-04-26 08:19:31 -0500

Seen: 68 times

Last updated: Apr 30