EnergyPlus Crashes with Desiccant System

asked 2024-04-10 05:00:02 -0500

Keigo's avatar

updated 2025-07-11 16:31:04 -0500

I want to model desiccant system, but EnergyPlus crashes. There is not so much information in the err file, and I got stuck. I'm not sure if the crash is due to a bug or my wrong setting. Any advice on how to resolve the crash would be appreciated. AirLoop and part of PlantLoop are as follows. The idf file (V24-1-0) is here.

image description

So far I have tried the following:

  • I tried with V23-2-0 and V24-1-0. Both crashed.
  • Desiccant system (the red part in the airloop in my sketch) was added to the AirLoop PAU_3-14_Tenant. Before I added the desiccant system, the simulation completed successfully.
  • CHP Hot HWloop was also added for regeneration air heating. I think Generator:MicroCHP is not the cause of the crash. It crached even if I changed the heating coil to Coil:Heating:Electric and removed CHP HWloop.
  • Precooling coil upstream of the desiccant system is not the cause of the crash. I tried removing it, but it still crashed.
  • It crashes during Air System Sizing, so I tried hardsizing everything. I ran simulation for Weather File Run Period only and did not run Sizing Calculation, System Sizing Calculation and Plant Sizing Calculation, but it still crashed.
edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
3

answered 2025-07-09 22:49:28 -0500

Keigo's avatar

updated 2025-07-10 01:13:37 -0500

Self-resolved. I updated the idf file to V25-1-0, and it no longer crashes. An err file was generated.

   ** Severe  ** Missing maximum humidity ratio setpoint (MaxHumRat) for 
   **   ~~~   ** Dehumidifier:Desiccant:System: PAU_3-14_TENANT DESICCANT SYSTEM
   **   ~~~   ** Node Referenced=PAU_3-14_TENANT HEAT RECOVERY SUPPLY OUTLET
   **   ~~~   ** use a Setpoint Manager to establish a "MaxHumRat" setpoint at the process air control node.
   **  Fatal  ** Previous severe set point errors cause program termination

The cause was that I was careless and put a setpoint manager for max humidity ratio to a wrong node. The simulation completed successfully after the location of the setpoint manager was revised.