** Severe ** vector too long

asked 1 year ago

Yagnik's avatar

updated 1 year ago

hello, I have assigned the AIrLoopHVAC with the Outdoorairsystem, humidifier, heating coil, cooling coil and fan on the branch, and am getting error like '* Severe * vector too long'. I have tried to understand the reason behind it, but yet I could not. could you please help me with it ?

Thanks in advance...

Preview: (hide)

Comments

@Yagnik can you upload your model to Google Drive, Dropbox, etc. and then share a URL for others to download? That would help others provide better solutions.

Aaron Boranian's avatar Aaron Boranian  ( 1 year ago )

1 Answer

Sort by » oldest newest most voted
1

answered 1 year ago

It's possible you are encountering an error that occurs when a zone or space has no surfaces; see here. There are some workarounds mentioned in that issue, and the issue has been resolved for the upcoming E+ 24.1 release.