AirChanges/Hour in EnergyPlus

asked 2023-10-11 12:03:24 -0500

updated 2023-10-11 20:51:37 -0500

Hi all,

I was wonderring if anyone knows what is the reference pressure for Air Change per Hour (ACH) under ZoneInfiltration:DesignFlowRate object.

More specifically, for AirChanges/Hour field, is the pressure difference based of 4 Pascals ACH or 50, ?

Thanks, Mohammad

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
2

answered 2023-10-11 15:09:29 -0500

updated 2023-10-11 15:10:18 -0500

The ACH should reflect expected pressure differences across the building envelope during normal occupation/operation (just like the 4x other "Design Flow Rate Calculation Methods"). So yes, closer to 4Pa (than 50Pa or 75Pa).

edit flag offensive delete link more

Comments

1

Thanks for your clarification.

Mohammad's avatar Mohammad  ( 2023-10-11 20:52:19 -0500 )edit