Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
0

AirChanges/Hour in EnergyPlus

asked 2023-10-11 12:03:24 -0600

updated 2023-10-11 20:51:37 -0600

Hi all,

I was wonderring if anyone knows what is the reference pressure for Air Change per Hour (ACH) under ZoneInfiltration:DesignFlowRate object.

More specifically, for AirChanges/Hour field, is the pressure difference based of 4 Pascals ACH or 50, ?

Thanks, Mohammad

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
2

answered 2023-10-11 15:09:29 -0600

updated 2023-10-11 15:10:18 -0600

The ACH should reflect expected pressure differences across the building envelope during normal occupation/operation (just like the 4x other "Design Flow Rate Calculation Methods"). So yes, closer to 4Pa (than 50Pa or 75Pa).

edit flag offensive delete link more

Comments

1

Thanks for your clarification.

Mohammad's avatar Mohammad  ( 2023-10-11 20:52:19 -0600 )edit

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Training Workshops

Careers

Question Tools

1 follower

Stats

Asked: 2023-10-11 12:03:24 -0600

Seen: 122 times

Last updated: Oct 11 '23