I want to override the temperature of surfaces (BuildingSurface:Detailed) with Schedule:File. I won't detail the reason here, but it's just for modelling simplification of high-rise buildings with conditioned floors and unconditioned floors.

image description

It's easy to set the floor/ceiling surfaces of the Typical floor as Adiabatic, but I want to do a little more accurate modeling.

When I look at the edd file, the Component Type "Surface" has only the following Control Types. I can't choose the surface temperature as Actuator.

  • Construction State,[ ]
  • ExteriorSurface Convection Heat Transfer Coefficient,[W/m2-K]
  • Interior Surface Convection Heat Transfer Coefficient,[W/m2-K]
  • View Factor To Ground,[ ]
  • Outdoor Air Drybulb Temperature,[C]
  • Outdoor Air Wetbulb Temperature,[C]
  • Outdoor Air Wind Speed,[m/s]
  • Outdoor Air Wind Direction,[degree]

Therefore, I came up with the following workaround.

I decided to override Outdoor Air Drybulb Temperature of the surface. Outside Boundary Condition of the surface was set to Outdoors (NoSun and NoWind). However, the surface temperature is different from the outdoor air temperature.

image description

In order to minimize the effect of the outside Air Film, Outside Convection Coefficient of the surface was set to 1000W/m2-K which is the maximum value that can be entered.

BuildingSurface:Detailed,
    2to50F_Office_1_Floor,  !- Name
    FLOOR,                   !- Surface Type
    Interior_Floor,   !- Construction Name
    2to50F_Office_1,  !- Zone Name
    ,                        !- Space Name
    Outdoors,                !- Outside Boundary Condition
    ,                        !- Outside Boundary Condition Object
    NoSun,                   !- Sun Exposure
    NoWind,                  !- Wind Exposure
    autocalculate,           !- View Factor to Ground
    4,                       !- Number of Vertices
    -154.48095703125,        !- Vertex 1 X-coordinate {m}
    -66.984489440917969,     !- Vertex 1 Y-coordinate {m}
    123.80000305175781,      !- Vertex 1 Z-coordinate {m}
    -155.17350769042969,     !- Vertex 2 X-coordinate {m}
    -64.064559936523438,     !- Vertex 2 Y-coordinate {m}
    123.80000305175781,      !- Vertex 2 Z-coordinate {m}
    -150.95506286621094,     !- Vertex 3 X-coordinate {m}
    -63.064018249511719,     !- Vertex 3 Y-coordinate {m}
    123.80000305175781,      !- Vertex 3 Z-coordinate {m}
    -150.26249694824219,     !- Vertex 4 X-coordinate {m}
    -65.983940124511719,     !- Vertex 4 Y-coordinate {m}
    123.80000305175781;      !- Vertex 4 Z-coordinate {m}

SurfaceProperty:ConvectionCoefficients,
    2to50F_Office_1_Floor,  !- Surface Name
    Outside,                 !- Convection Coefficient 1 Location
    Value,                   !- Convection Coefficient 1 Type
    1000;                    !- Convection Coefficient 1 {W/m2-K}

After that, I wrote a small EMS program to override the Outdoor Air Drybulb Temperature. The simulation result looks ok. The surface temperature became almost the same value as the temperature in Schedule:File.

Is there a better way to override the surface temperature?

edit retag flag offensive close merge delete

Comments

1

Hey @Keigo. Did you consider OtherSideCoefficients as an option? From what you describe, I think it could be easier - no need to bring in EMS. Maybe I'm missing something.

Denis Bourgeois's avatar Denis Bourgeois  ( 2023-09-16 15:29:22 -0500 )edit

@Denis Bourgeois I want all the conditioned floors on the left side of the atachetd image to be represented by one typical floor with multiplier on the right. It is very difficult to properly adjust the heat transfer coefficient of the floor/ceiling of the typical floor on the right because the typical floor is adjacent to outdoors while the actual conditioned floors on the left are not exposed to outdoors. There is heat transfer between the conditioned floor and the unconditioned floor. I want to take the heat transfer into account with one typical floor model.

Keigo's avatar Keigo  ( 2023-09-16 18:57:48 -0500 )edit

@Keigo the OtherSideCoefficients object type has a constant temperature field for "...either of the surface or outside air temperature." This can also be defined via schedule. The tricky part is knowing what value to apply to all the other heat transfer parameters of the object.

Aaron Boranian's avatar Aaron Boranian  ( 2023-09-18 09:35:22 -0500 )edit

Also, wouldn't you want an unmultiplied top and bottom floor surrounding the multiplied typical floor in the middle? The typical floor should be adjacent to outdoors only at the walls, not the floor or ceiling surfaces.

Aaron Boranian's avatar Aaron Boranian  ( 2023-09-18 09:36:34 -0500 )edit