Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
1

Optimum Start for VRF

asked 2023-09-08 13:05:37 -0500

apdavis's avatar

updated 2023-09-08 18:51:10 -0500

Is there a way to apply optimum start to an OpenStudio building model with VRF?

I've used the air loop availability manager for Optimum Start for other HVAC systems, but I'm wondering if there's a way to model it on a VRF system specifically

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
2

answered 2023-09-09 01:53:39 -0500

ZoneHVAC:TerminalUnit:VariableRefrigerantFlow has an Availability Manager List Name

But the field is not wrapped in the OpenStudio SDK. So you'll need to use an EnergyPlusMeasure.

You could go upvote the feature request too if that's important to you: https://github.com/NREL/OpenStudio/is...

edit flag offensive delete link more

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Training Workshops

Careers

Question Tools

1 follower

Stats

Asked: 2023-09-08 13:05:37 -0500

Seen: 60 times

Last updated: Sep 09 '23