Optimum Start for VRF

asked 2023-09-08 13:05:37 -0600

apdavis's avatar

updated 2023-09-08 18:51:10 -0600

Is there a way to apply optimum start to an OpenStudio building model with VRF?

I've used the air loop availability manager for Optimum Start for other HVAC systems, but I'm wondering if there's a way to model it on a VRF system specifically

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
2

answered 2023-09-09 01:53:39 -0600

ZoneHVAC:TerminalUnit:VariableRefrigerantFlow has an Availability Manager List Name

But the field is not wrapped in the OpenStudio SDK. So you'll need to use an EnergyPlusMeasure.

You could go upvote the feature request too if that's important to you: https://github.com/NREL/OpenStudio/is...