SEER and HSPF in E+/Design Builder

asked 2023-08-09 21:06:25 -0600

Anna's avatar

updated 2023-08-10 08:18:08 -0600

Has anyone observed a big difference between SEER/HSPF reported in the Equipment Summary report ( E+/Design Builder) and rated SEER/HSPF ? I typically enter COP, adjusted by removing fan energy per the equations in Section 11 of ASHRAE Std 90.1-2019. Or, when information is available, I use manufacturers data to calculate COP as a ratio of the cooling capacity and system power, where system power includes only outdoor fan and compressor, at rated conditions. Either way, the Equipment Summary always reports SEER /HSPF much lower than the rated equipment SEER/HSPF. The difference is significant. For example, a heat pump rated at 16 SEER/ 8.0 HSPF would show up in the Equipment Summary as having less than 12 SEER/5.5 HSPF. I derived performance curves for several Heat Pumps, but this did not close the gap or mitigate the issue. Based on conversation with Design Builder support, at some point I believed this may have to do with weather file. However, whatever weather file (location) I run, my SEER/HSPF in the Equipment Summary are always significantly lower than the rated values.
Could someone explain why this might be happening? Residential projects that I work on typically use Heat Pumps for apartments conditioning (150-300 Heat Pumps per building), so obviously this discrepancy may have a big impact on the energy results for this type of projects. Any insight, recommendation, comments you could provide would be much appreciated!

Anna

edit retag flag offensive close merge delete

Comments

Anna, did you enter the coil model fan performance for SEER calculations? or leave that field blank (which would use the default)?

rraustad's avatar rraustad  ( 2023-08-10 09:05:44 -0600 )edit

Hi Richard, Yes , I entered the evaporator fan power w/cfm for this specific HP model. This increased SEER a little bit, but it's still much lower than 16 SEER. I also ran a simulation with my electric resistance heating capacity set to zero, to see if HSPF would change, but it did not. The heating energy went down a little bit, but not as much as I would expect for climate zone 5B.

Anna's avatar Anna  ( 2023-08-10 10:32:09 -0600 )edit

The only thing I can suggest is to send an idf that looks wrong and include manufacturers data if possible.

rraustad's avatar rraustad  ( 2023-08-10 12:51:30 -0600 )edit

Hi Richard, Here is the link to IDF and manufacturer data: https://jordanskala-my.sharepoint.com...

The model has several systems, but only 3 systems (1.5 ton, 2.0 ton, and 2.5 ton) have custom curves: AH R-SW 1.5 TON, AH R-SE 2.0 TON, and AH R-SW1 2.5 TON. Per AHRI ratings, these Heat Pumps-splits should have the efficiency 14.3 SEER2– 15 SEER2 ( 15.0-15.8 SEER) and 7.5 HSPF2 (8.8 HSPF); however, the equipment summary report is showing 13.7-16 SEER and 5.5 HSPF. Any insight you could provide will be much appreciate.

Anna's avatar Anna  ( 2023-08-21 20:07:41 -0600 )edit

This is a V9.4 input file. Have you considered downloading the latest executable and seeing if the answer is the same? I see the 11.7 SEER for L3XRES:L3XRXSW PTHP DX COOLING COIL but this could be the older calculations, which could have been corrected, or bad performance curves, where did those come from? I tried updating the file to V22.2 and V22.3 but ran into an issue.

rraustad's avatar rraustad  ( 2023-08-22 21:15:27 -0600 )edit

1 Answer

Sort by » oldest newest most voted
0

answered 2023-08-10 05:13:29 -0600

Jim Dirkes's avatar

Anna, I don't think the weather file has anything to do with the SEER or HSPF calculations, Their test conditions are set by AHRI, not weather. I may be able to help you with some derivations I use if you contact me directly.

edit flag offensive delete link more

Comments

Hi Jim,

Thanks for your response! I read that SEER for Multi Speed DX coil and HSPF are supposed to be calculated as weighted average for various outdoor air bin temperatures, so I was wondering if E+ is looking at the actual weather file to calculate the capacity and electricity consumed whenever the system falls into the given temperature bin and using those numbers to calculate SEER/HSPF. Just to clarify, I need to model Single-Speed Heat Pumps, 1 to 2.5 ton. Have you ever seen the Equipment Summary report showing SEER higher than 13 and HSPF higher than 5.5 for Heat Pumps ( <65 kBtu/h).

Anna's avatar Anna  ( 2023-08-10 08:59:37 -0600 )edit

Anna, the "various outdoor air temperatures" are specific values that are independent of the climate. Single speed heat pumps in E+ have HSPF calculated properly - two speed are not included (I'm pretty sure; same for DX coil EER) I have an Excel macro prepared by the fellow who wrote the E+ HSPF code (Chandan Sharma) that works very well. He has told me that I may share it, if you'd like a copy.

Jim Dirkes's avatar Jim Dirkes  ( 2023-08-10 09:09:32 -0600 )edit

Sure, I would appreciate that very much. Could you share the link here, or should I provide my email address? I'm just trying to understand the equations behind E+ calculations, so that I can model equipment correctly.

Anna's avatar Anna  ( 2023-08-10 10:09:10 -0600 )edit

Here is my email address, if you don't mind sharing the file:

Anna's avatar Anna  ( 2023-08-10 10:35:21 -0600 )edit