thermal zone design for VRF HVAC

asked 2023-05-15 01:18:52 -0600

panda rose's avatar

updated 2023-05-15 09:23:32 -0600

I want to run a simulation for a selected zone in a buliding by E+. The target zone is set specific geometric info, but the rest zones of different floors are gathered into one big zone due to unknown geometric info. Does this kind of design for Non-target zones influence the accuracy of target zone simulation?

P.S: The HVAC system of building is created by mutil VRFs(outdoor units/indoor units). The target zone has its own outdoor unit and indoor units ,which have no relationship with that of Non-target zones.

edit retag flag offensive close merge delete

Comments

I am new in unmethours, sorry for sendding the same content. I have deleted the old one. Please let this question can be seen from other people. Best regards;

panda rose's avatar panda rose  ( 2023-05-15 07:40:53 -0600 )edit

1 Answer

Sort by » oldest newest most voted
2

answered 2023-05-29 03:42:56 -0600

Keigo's avatar

If the geometry or heat gain of the rest zones adjacent to the target zone is unknown, I reccoment you should set Outside Boundary Condition of Surfaces between the rest zones and the target zone to Adiabatic to eliminate uncertainty.

edit flag offensive delete link more

Comments

@Keigo Nomura Dear Nomura-san: Thank you for your answer. I got it.

Best regards;

panda rose's avatar panda rose  ( 2023-06-05 19:32:01 -0600 )edit