Fan power settings of parallel VAV Fan-powered boxes in E+
Hi Guys: Does any body know how to set "Maximum Primary Air Flow Rate" ,"Maximum Secondary Air Flow Rate" ,"Minimum Primary Air Flow Fraction" and "Fan On Flow Fraction" in energyplus to meet G3.1.3.14 "----" Fans in parallel VAV fan-powered boxes shall be sized for 50% of the peak design flow rate and shall be modeled with 0.74 W per L/s fan power. Minimum volume setpoints for fan-powered boxes shall be equal to 30% of peak design flow rate"?
Added "appendix-g" tag and changed G3.1.3.15 to G3.1.3.14 which corresponds to 90.1-2007, 2010, and 2013.
Note that the control of fan powered boxes according to PNNL 90.1 PRMRM guidance: 2010: https://www.pnnl.gov/main/publication... 2016: https://www.pnnl.gov/main/publication...
was fixed in E+ v8.7. https://github.com/NREL/EnergyPlus/pu...