Fan power settings of parallel VAV Fan-powered boxes in E+

asked 2014-10-30 04:58:01 -0600

hutiejun1223's avatar

updated 2014-10-30 07:55:41 -0600

Hi Guys: Does any body know how to set "Maximum Primary Air Flow Rate" ,"Maximum Secondary Air Flow Rate" ,"Minimum Primary Air Flow Fraction" and "Fan On Flow Fraction" in energyplus to meet G3.1.3.14 "----" Fans in parallel VAV fan-powered boxes shall be sized for 50% of the peak design flow rate and shall be modeled with 0.74 W per L/s fan power. Minimum volume setpoints for fan-powered boxes shall be equal to 30% of peak design flow rate"?

edit retag flag offensive close merge delete

Comments

Added "appendix-g" tag and changed G3.1.3.15 to G3.1.3.14 which corresponds to 90.1-2007, 2010, and 2013.

MatthewSteen's avatar MatthewSteen  ( 2014-10-30 07:55:24 -0600 )edit

Note that the control of fan powered boxes according to PNNL 90.1 PRMRM guidance: 2010: https://www.pnnl.gov/main/publication... 2016: https://www.pnnl.gov/main/publication...

was fixed in E+ v8.7. https://github.com/NREL/EnergyPlus/pu...

DavidReddy's avatar DavidReddy  ( 2018-05-08 14:09:17 -0600 )edit

2 Answers

Sort by » oldest newest most voted
2

answered 2014-10-30 08:05:31 -0600

updated 2014-10-30 08:31:17 -0600

For air flow it looks like you can set the air flow using the fields for these objects.

AirTerminal:SingleDuct:ParallelPIU:Reheat

AirTerminal:SingleDuct:SeriesPIU:Reheat

For fan power you can adjust the pressure rise to predict the W and W/L/s output from EnergyPlus. See the question below for resources.

Fan Power Inputs in OpenStudio

edit flag offensive delete link more
1

answered 2015-10-28 12:12:06 -0600

Gio's avatar

Hi! I set them as Autosize. Then I checked the results for "Maximum air flow" for every parallel box: I calculated 50% for every peak and I multiplied it for 0.74, therefore I obtained the power to set. Finally I used a simple proportion ("pressure input"/"power output Autosize simulation"="X"/"power calculated for G3.1.3.14") to obtain the right pressure rise to set for all the fans to get the power previously calculated. Using the equation is absolutely correct but if you don't change the efficiencies it should simply work with a proportion. I also set the fan percent to air flow to 0.

edit flag offensive delete link more