Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
0

Inconsistent crash without error log

asked 2023-04-26 05:39:00 -0500

updated 2023-04-26 10:50:11 -0500

hi

My simulation is crashing halfway through, and the error log is empty, completely blank. I'm using EnergyPlus 22.2. I've checked multiple times the IDF and I can't seem to find any reason causing this. I've tried with an original EPW and another one modified through Elements. Both crashed.

Please find attached the IDF and the epws. https://we.tl/t-twcYLtNGjU

has anyone experienced something similar? any help would be really appreciated.

kind regards, Olivier

edit retag flag offensive close merge delete

2 Answers

Sort by ยป oldest newest most voted
2

answered 2023-04-26 14:46:05 -0500

I got the same message as @Denis Bourgeois. After fixing that (when not running using EP-Launch), by running ExpandObjects.exe and then changing expanded.idf to in.idf, the file ran successfully with these results. If you are running the file and not getting these results you may have a memory issue.

Program Version,EnergyPlus, Version 23.1.0-a116efebd3, YMD=2023.04.26 15:25,
   ** Warning ** Version: in IDF="22.2" not the same as expected="23.1"
   ** Warning ** Version: in IDF="22.2" not the same as expected="23.1"
   ************* Beginning Zone Sizing Calculations
   ** Warning ** Weather file location will be used rather than entered (IDF) Location object.
   **   ~~~   ** ..Location object=SITE 1
   **   ~~~   ** ..Weather File Location=Abuenas.Ardeche.Meridionale.AP AR FRA SRC-TMYx WMO#=075700
   **   ~~~   ** ..due to location differences, Latitude difference=[44.54] degrees, Longitude difference=[4.37] degrees.
   **   ~~~   ** ..Time Zone difference=[1.0] hour(s), Elevation difference=[28000.00] percent, [280.00] meters.
   ** Warning ** ProcessScheduleInput: Schedule:Constant="ALWAYS OFF DISCRETE", Blank Schedule Type Limits Name input -- will not be validated.
   ** Warning ** WindowMaterial:Blind="FIXEDWESTBLINDS", Slat Angles/Widths
   **   ~~~   ** Slat Width [2.00E-002] is less than Slat Separation [6.00E-002].
   **   ~~~   ** This will allow direct beam to be transmitted when Slat angle = 0.
   ** Warning ** GetHTSurfaceData: Surfaces with interface to Ground found but no "Ground Temperatures" were input.
   **   ~~~   ** Found first in surface=ROOM_1EDE771E..FACE_8242890E
   **   ~~~   ** Defaults, constant throughout the year of (18.0) will be used.
   ** Warning ** CheckUsedConstructions: There are 16 nominally unused constructions in input.
   **   ~~~   ** For explicit details on each unused construction, use Output:Diagnostics,DisplayExtraWarnings;
   ** Warning ** GetShadowingInput: The shading transmittance for shading devices changes throughout the year. Choose DetailedSkyDiffuseModeling in the ShadowCalculation object to remove this warning.
   **   ~~~   ** Simulation has been reset to use DetailedSkyDiffuseModeling. Simulation continues.
   **   ~~~   ** Better accuracy may be gained by setting the Shading Calculation Update Frequency to 1 in the ShadowCalculation object.
   ** Warning ** DetermineShadowingCombinations: There are 2 surfaces which are receiving surfaces and are non-convex.
   **   ~~~   ** ...Shadowing values may be inaccurate. Check .shd report file for more surface shading details
   **   ~~~   ** ...Add Output:Diagnostics,DisplayExtraWarnings; to see individual warnings for each surface.
   ** Severe  ** DetermineShadowingCombinations: There are 2 surfaces which are casting surfaces and are non-convex.
   **   ~~~   ** ...Shadowing values may be inaccurate. Check .shd report file for more surface shading details
   **   ~~~   ** ...Add Output:Diagnostics,DisplayExtraWarnings; to see individual severes for each surface.
   ** Warning ** DeterminePolygonOverlap: Too many figures [>15000]  detected in an overlap calculation. Use Output:Diagnostics,DisplayExtraWarnings; for more details.
   ** Warning ** GetSimpleAirModelInputs: ZoneInfiltration:DesignFlowRate="ROOM_44AC0377_SPACE EN-RESIDENTIAL::DETACHEDHOUSE_INFILTRATION 1", Design Flow Rate Calculation Method specifies Flow Rate per Exterior Surface Area, but Exterior Surface Area = 0.  0 Infiltration will result.
   ** Warning ** GetSimpleAirModelInputs: ZoneInfiltration:DesignFlowRate="ROOM_8561C570_SPACE EN-RESIDENTIAL::DETACHEDHOUSE_INFILTRATION 1", Design Flow Rate Calculation Method specifies Flow Rate per Exterior Surface Area, but Exterior Surface Area = 0.  0 Infiltration will result.
   ** Warning ** GetSimpleAirModelInputs: ZoneInfiltration:DesignFlowRate="ROOM_2E48DDB6_SPACE EN-RESIDENTIAL::DETACHEDHOUSE_INFILTRATION 1", Design Flow Rate Calculation Method specifies Flow Rate per Exterior Surface Area, but Exterior Surface Area = 0.  0 Infiltration will result.
   ** Warning ** GetSimpleAirModelInputs: ZoneInfiltration:DesignFlowRate="ROOM_B1E4A21E_SPACE EN-RESIDENTIAL::DETACHEDHOUSE_INFILTRATION 1", Design Flow Rate Calculation Method specifies Flow Rate per Exterior ...
(more)
edit flag offensive delete link more
0

answered 2023-04-26 13:48:46 -0500

updated 2023-04-26 13:53:52 -0500

Failed to launch altogether, not halfway through. An excerpt of the generated "eplusout.err" file (when running the IDF with either EPW file):

** Severe  ** GroundHeatTransfer:* objects [...] not supported directly by EnergyPlus.
**   ~~~   ** You must run the ExpandObjects program on this input.

As mentioned elsewhere (e.g. here and here), you need to first run the Basement preprocessor program.

edit flag offensive delete link more

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Training Workshops

Careers

Question Tools

1 follower

Stats

Asked: 2023-04-26 04:01:56 -0500

Seen: 169 times

Last updated: Apr 26 '23