not fully enclosed and heating load
Hi,
I have two questions:
- one of my zone is not fully enclosed and there is some errors message but I dont understand the meaning
- calculated design heat load is zero, we are here not use heating load. How to solve this error?
Please see EnergyPlus error file below
Program Version,EnergyPlus, Version 9.5.0-de239b2e5f, YMD=2023.04.20 16:19,
************* Beginning Zone Sizing Calculations
** Warning ** CalculateZoneVolume: The Zone="KM WC LT2" is not fully enclosed. To be fully enclosed, each edge of a surface must also be an edge on one other surface.
** ~~~ ** The zone volume was calculated using the floor area times ceiling height method where the floor and ceiling are the same except for the z-coordinates.
** ~~~ ** The surface "A8329B" has an edge that is either not an edge on another surface or is an edge on three or more surfaces:
** ~~~ ** Vertex start { 0.1234, 4.3450, 6.9800}
** ~~~ ** Vertex end { 0.1234, 4.3450, 3.6000}
** ~~~ ** The surface "91CD98" has an edge that is either not an edge on another surface or is an edge on three or more surfaces:
** ~~~ ** Vertex start { 0.1234, 6.2450, 3.6000}
** ~~~ ** Vertex end { 0.1234, 6.2450, 6.9800}
** ~~~ ** The surface "97F56C" has an edge that is either not an edge on another surface or is an edge on three or more surfaces:
** ~~~ ** Vertex start { 0.1234, 6.2450, 6.9800}
** ~~~ ** Vertex end { 0.1234, 4.3450, 6.9800}
** ~~~ ** The surface "97F56C" has an edge that is either not an edge on another surface or is an edge on three or more surfaces:
** ~~~ ** Vertex start { 0.1234, 4.3450, 3.6000}
** ~~~ ** Vertex end { 0.1234, 6.2450, 3.6000}
** Warning ** Calculated design heating load for zone=K TIDUR LT1 is zero.
** ~~~ ** Check Sizing:Zone and ZoneControl:Thermostat inputs.
** Warning ** Calculated design heating load for zone=R KELUARGA is zero.
** ~~~ ** Check Sizing:Zone and ZoneControl:Thermostat inputs.
** Warning ** Calculated design heating load for zone=KAMAR TIDUR LT2 is zero.
** ~~~ ** Check Sizing:Zone and ZoneControl:Thermostat inputs.
** Warning ** Calculated design heating load for zone=KAMAR TIDUR UTAMA is zero.
** ~~~ ** Check Sizing:Zone and ZoneControl:Thermostat inputs.
** Warning ** Calculated design heating load for zone=VOID is zero.
** ~~~ ** Check Sizing:Zone and ZoneControl:Thermostat inputs.
thank you very much in advance where I can send the idf files for your checking
regards, Budijanto Chandra
@budich you can upload your IDF to a file-sharing service like Dropbox or Google Drive, then edit your post to include the URL to your uploaded file(s).
this is the link https://drive.google.com/drive/folder... thank you very much have a nice day